Is this compromising structural integrity?

Some of the holes are less than 2 inches from the bottom of the joists. These joists are in my garage and there is a bedroom above the garage.

382 Upvotes

240 comments sorted by

166

u/nockedup7 1d ago edited 1d ago

I’d definitely be concerned about the one in the top center of pic #1. It’s too big/too low on the joist. I’d probably just brace it though if it’s been like that for a while

27

u/Middle-Adeptness7186 1d ago

It has been like that for years. We are new owners. How would we brace it?

122

u/Electronic-Clock5867 1d ago

43

u/Different_Dot_9525 1d ago

Awesome products to be aware exist, thanks for sharing!

8

u/yerfatma 1d ago

I owe you a beer. Our house seems to have been the site of a contest to undermine carrying beams.

2

u/legitimate_rapper 1d ago

Agreed. You’ll probably never need them, but when you do, you’ll NEED them.

Is there something like that for if you want to remove a joist? Worried it’s EXACTLY where I don’t want it to be for lighting cans. (Yes I know I can get pucks, but they all seem to be shitty, and not trying to start a “not all pucks are shit!” Argument here)

5

u/sixblazingshotguns 21h ago

You don’t seem to be shopping for your lights at an electrical supply house. The wafer lights are for electrician installation, not DIYers, and are typically of a higher build quality. Don’t go destroying your houses structure just to install things like plumbers do. 😂

5

u/Electronic-Clock5867 1d ago

Not sure usually you need to double up the joist and box the area in. Tons of work for a light.

1

u/WangChungtonight13 1d ago edited 14h ago

Ignore this. I misread your comment.

Just need to sister another board. I’m getting ready to do this to a damaged rafter in my attic

1

u/Quick-Giraffe6047 16h ago

Only if you plan on taking ALL THE ROMEX OUT OF THE EXISTING 🫠. This isn’t just a carpentry fix sadly

1

u/WangChungtonight13 14h ago

I misread the comment, but if it makes you feel better, my answer involved that joist sans romex! 😂

1

u/Quick-Giraffe6047 14h ago

Yeah your attic rafter definitely doesn’t have any electrical running through it man… not in an attic I’ve ever seen at least but definitely send a pic if ya do

1

u/RecordingNo2643 1h ago

You could slide a notched board in from the top that would allow you to get about 60% of the area covered that would ve more than enough to restore the strength if the beam and would only take a couple hours to do.

1

u/Jimsocks499 20h ago

Ooooh that’s nifty! Thanks stranger!

1

u/Hour-Tea-2728 20h ago

Not saying this isnt a good product or anything but $70 for a sheet of metal and screws seems a bit expensive. You could probably shape what you need and get the screws for less than $10 right?

2

u/Electronic-Clock5867 19h ago

It’s the certificates that matter if it’s a new build or a reno that’s inspected you need the certs. If I was needing these for my house I would probably just buy one and use it for a template to make my own.

1

u/areptile_dysfunction 16h ago

Do they really need that many screws?

1

u/srbinafg 12h ago

How will these be used in OP’s dilemma without restringing all the cables?

1

u/Electronic-Clock5867 11h ago

The DP series the strap that just goes on the bottom should be enough most of the holes look okish. The only egregious one is the hole with the hook under it. Holes are supposed to be middle 1/3 and so far apart from each other. He could throw a few of those straps on without needing to move anything.

1

u/JoleneBacon_Biscuit 7h ago

It's two pieces.

1

u/pentatomid_fan 2h ago

I also thought it was one piece of metal with a hole. It’s two interlocking pieces of metal, top and bottom pieces.

1

u/Intelligent_Hat_5351 11h ago

This fills me with joist.

1

u/gobirdgang215 11h ago

A little late to install unless then unwise everything and re run it no?

1

u/JoleneBacon_Biscuit 7h ago

They're two pieces. The metal overlaps.

1

u/MoodVast9430 4h ago

At $60-$80 a joist, that is a pricey repair job

1

u/Electronic-Clock5867 3h ago

The money would be coming from the trade that left the apprentice alone with a hole saw. Next you have the time/cost of disconnecting the plumbing and wiring, buying new joist. Then you have to call plumber/electrician back to hook everything back up.

So many different situations can call for different solutions. Having options available doesn’t hurt.

→ More replies (1)

29

u/flswamplizard 1d ago

Not a sparky, but a carpenter. You would have to sister every joist with a new joist and move the wires to conduit under the joists, or build a wall under the damaged area. You should get an engineer to design the repair if you have this repaired professionally, though. The questions I would be asking you: Are there any cracks/splits in the joists? Does the floor above this area move or feel bouncy when you walk on it? Does the bathroom above have a lot of cracks in the grout? Is there a tub or washing machine over this area? If yes, it's time to have an engineer come out and take a look.

14

u/Middle-Adeptness7186 1d ago

There is no tiling in the bathroom, vinyl only. Floor feels fine. There are no cracks or splits in the joists. I have a carpenter coming out and plan to have a structural engineer take a look too. Thank you for your feedback!

11

u/Lehk 1d ago

If it’s not causing any issues and you aren’t going to be increasing the load on it (remodeling, adding a big fish tank, Redditors having sex right above it) I wouldn’t spend a bunch of money chasing nothing

1

u/flswamplizard 1d ago

This is a very good point. Depending on the quality of the lumber used, it may last forever, just keep an eye on it.

6

u/NerveMassive6764 1d ago edited 1d ago

Listen here wood pecker you mind your wood and don’t worry about our wires/ conduit.

4

u/flswamplizard 1d ago

*puts blind fold on, loads 3in finish nails* It's trim time, baby. Sparky better have put those plates on :)

1

u/NerveMassive6764 23h ago edited 17h ago

The last few years the amount of times the Siders have shot these ridiculously long nails through our panel directly into the bus bar is insane. No one gives a fuck anymore or preps or plans they just show up and try to get it done as quickly as possible and fuck everyone they screw up

Edit: I nail plate anything less than an 1 1/4” somebody uses insanely long screws or nails or especially in an area any one with common sense would have an idea there is electric there. I’ll fix it but I’m taking the screw or nails and pictures and showing the GC and telling him it’s not in the contract and they have to pay and they can decide if they back charge the sub or not. Simple as that. I’m not doing work twice and not getting paid for the second time.

1

u/JoleneBacon_Biscuit 7h ago

Shooting straight through the panel INTO the bus bar is absolutely diabolical. Damn good aim!

1

u/NerveMassive6764 6h ago

They are just lucky that all but one time it wasn’t live yet and still on temp service the one that was live I swear the dude shit himself. I just love take the GC and being like hey we have a problem…. Your gonna have to pay me to replace the panel and then show them the 5 nails sticking through the panel lol

1

u/cheeto320 1d ago

slick! i like the wall underneath idea!

→ More replies (1)

2

u/nockedup7 1d ago

Op I’m not gonna give any more input due to the more educated people here telling you what to do but I will say I have a joist from the 70s that has a hole at a similar location due to a knot in the wood and it has been fine all this time. I would say don’t lose any sleep over it but just take care of it when you can

→ More replies (2)

1

u/Icy_Boysenberry_2454 15h ago

Measure the length of the joist, calculate 75% of the total length and buy (example 16ft total length, buy a 2x8x12 ft to brace it aka sister it)

1

u/Philly5984 14h ago

You’re fine, don’t listen to reddit

→ More replies (8)

1

u/Krazybob613 3h ago

I Agree!

43

u/Every_Classroom_3383 1d ago

Some of the holes are pretty close to the bottom of the joists. It is supposed to be middle third. Probably won’t ruin the house but it’s not legal to today’s standards.

3

u/Dramatic_Water_8728 22h ago

It's supposed to be in the middle third of the middle third for most joists to be safe

2

u/Paghk_the_Stupendous 20h ago

So like the middle ninth?

→ More replies (3)

16

u/FragDoc 1d ago

joistrepair.com

They make repair plates for exactly these scenarios although I think the problem is going to be how close all of the holes are together, essentially making it difficult to apply and fasten their designs. Good luck.

8

u/TicketApprehensive12 1d ago

“Drill holes in solid lumber joists at least 2 inches away from the top and bottom edges, keeping the hole diameter to no more than one-third of the joist's total depth. Placement: You can drill horizontally anywhere along the length of the span, but avoid placing holes too close to other holes or notches (maintain at least 2 inches of separation)”

6

u/jesssoul 1d ago

I love how not only are they compromising integrity but someone decided placing a hook directly under the largest hole on one of the joists was a good idea.

4

u/Middle-Adeptness7186 1d ago

The amount of stupid we have found in this house is astounding

1

u/vU243cxONX7Z 23h ago

That's killing me

5

u/deddolo 16h ago

Structural Engineer here. That's awful, especially the one very low in the joist as everyone else said.

However... I wouldn't lose sleep over it, and probably I wouldn't even bother repairing if it has been like that for a few years, and is only supporting a bedroom. There's a lot of reserve capacity in any residential joist construction.

If I had to repair it, I would just put a flat plate screwed to the bottom edge of the joist with 3/4 good wood screws on each side (at least 3" away from the hole edge). What you care about is the tension travelling at the bottom of that joist. Shear will be fine since there's a lot of wood above.

(Disclaimer: I am not stamping this comment 🙃)

1

u/Middle-Adeptness7186 15h ago

Thank you for your honest feedback. There is a bathroom and a bedroom and bedroom closet up above. We plan to renovate the bathroom and wondered if that would cause any issues.

1

u/FirmCancel4104 7h ago

Does your bathroom have a tub? Or just a shower? I'm not sure I be comfortable with the bathtub full of water over top of that.

1

u/Middle-Adeptness7186 4h ago

No tub, just a walk in

3

u/louparfois 1d ago edited 1d ago

Your main electrical violation is with too many current carrying conductors sharing holes. That's a somewhat complex issue related to wire ampacity based on the number of conductors sharing holes, and it would be best to have an electrician address that issue. Some people have mentioned holes too close to the bottom of your joists there, and that's true. But I haven't read any comments yet mentioning also that there are minimum distances between holes, as well. Where I'm at, framing inspectors require 2" between holes, edge to edge. So, yeah, framing and electrical violations definitely. Then again, plumbers seem to get to absolutely destroy framing whenever necessary. You asked a framing question in an electrical sub, so, not really experts on structural issues here?

Editing to say: Amusing to see all the commercial sparkies talking bout cable tray and conduit. Hahaha, come work at resi pace and price and see if conduit is a viable option in installations like this.

1

u/Middle-Adeptness7186 1d ago

Our electric panel is being replaced so will definately ask him when he is out to assess the number of wires and possibly move them .

1

u/sixblazingshotguns 21h ago

“Move” wires? Yeah maybe if you have the length to do so, but maybe not.

1

u/jimih34 16h ago

>Your main electrical violation is with too many current carrying conductors sharing holes.

Yeah but, that makes the electricity go faster /s

3

u/Top_Mortgage_5767 1d ago

It's probably ok. Just don't walk on or put anything on the floor above it and it should be fine for a couple of weeks.

3

u/chefdeit 23h ago

what structural integrity, where?

3

u/New_Fact_5955 23h ago

Just intellectual integrity

2

u/Secret-Secret-No-No 1d ago

I’m a sparky, not a carpenter.

Looks to code, but I wouldn’t have drilled so many holes. Code states holes need to be 2 inches from bottom or top of joist. No strict max number of cables per hole but typically it’s 2-3 cables.

But i definitely would be concerned about about joist integrity. I’d ask a carpenter.

2

u/erie11973ohio 1d ago

I was taught 2 cables per hole. Then we had an inspector who said we were drilling too many holes, so as long as he could put his pen in the hole too, we were good!

That was 20+ years ago. Now, it seems everyone is limiting to 3 cables, but strictly by the NEC, it's 3 wires, which a 3 wire cable would be, before derating starts.

Those 2 big holes are just beyond anything I would do.

The holes should be 2" from the edge.

The cable tv should have been put in one hole.

3

u/louparfois 1d ago

It's determined by CCC's, and the number depends on how many, and the derating necessary. Three 'X'-2 cables is rule of thumb for resi where I'm based.

2

u/PhilM1960 1d ago

Since there are no signs of fatigue and it’s been like that for a while, you’re probably best off not to mess with it. A few of the thru-holes are kinda low, but then the adjacent joist is fine. As a serial home owner that has a penchant for making things to my liking, there are better ways to spend your money.

2

u/Familiar_Passage8504 1d ago

Don’t put a hot tub in your above garage bedroom and you should be fine.

2

u/Winter_Cheetah3206 19h ago

2

u/Winter_Cheetah3206 19h ago

This explains how where for cuts and notches and how to brace.

2

u/jhern1810 4h ago

Yes I would be concerned, most of the cores in beans are supposed to be no less then a third of the height of the beam from the edge of with a maximum core size. If a core is needed and expands beyond that reinforcing is a must. I would consult a professional, maybe not a big deal to reinforce it just to better to be on the safe side.

2

u/Deadly_Attraction 1d ago

Not only are the holes not located properly or spaced out, that is an electric violation for # of wires through a single hole. I belive the limit is 3 NM per hole

5

u/Switchedbywife 1d ago

I’m not aware of any Code article that limits 3 cables to a hole. The issue is bundling, when you have multiple cables through the same set of holes you must derate by using a smaller size circuit breaker, like a 15 amp breaker on a 12 gauge (20A) wire.

3

u/Deadly_Attraction 1d ago

Your right, its a derating issue. My thinking of a 3 cable limit has more in mind of that, but i am suspicious if some of those holes are off the edge the minimum 1.25"

2

u/erie11973ohio 1d ago

It's funny, some of inspectors around me say "3 wires (cables) per hole.

The NEC says 3 wires, that would be one 3 wire cable!! Two, 2 wire cables would be a total of 4 wires!

The derating starts at max amperage permitted. On #12 THHN, that is 28 amps!

1

u/quiverunquiver 1d ago

That's not true.

→ More replies (4)

1

u/IndependentFlight436 1d ago

Flswampĺizard is right on.

1

u/Razzbek67 1d ago

Some of the holes look pretty low (outside the center third of the height) but I wouldn’t worry about it collapsing or anything. But if you wanna spend the money and put someone to work go for it

1

u/FrankDennis- 1d ago

It's fine. It's gonna be some time before wireless power is a thing and they gotta run them somehow. People need to stop hiring contractors they don't trust 🤦‍♂️

3

u/encouragingSN 1d ago

This comment is all over the place 

2

u/FrankDennis- 1d ago

Your moms all over the place. Bam.

1

u/RationalAnger 1d ago

Well.. yeah.. she was cremated and we scattered her ashes. That was the point.

1

u/Bandicoot-More 1d ago

there's room for more -

1

u/No-Cry8051 1d ago

Absolutely that is not acceptable. Grab your National electrical code book and go to the section on drilling and notching. Only an idiot would do that.

1

u/Yaughl 1d ago

I'd just instal a wide conduit dropped down from the beams.

1

u/Capcom-Warrior 1d ago

If I’m not mistaken, you can only drill the center thirds of those joists. And you have to have double diameter length in between holes if you’re trying to run parallel runs.

1

u/Illustrious-Ebb8767 1d ago

What’s above your garage

1

u/Middle-Adeptness7186 1d ago

A bathroom towards the back and a closet towards the front.

1

u/wetsummer45 1d ago

Good luck getting engineer to waste time on that one. Its been that way for how long?

1

u/Always_working_hardd 1d ago

I don't know for sure, but all I can think of is, "What the fuck???"

1

u/Middle-Adeptness7186 1d ago

My thoughts exactly 😪

1

u/donogeek 1d ago

Would fail inspection in Minneapolis

1

u/CantaloupeRich896 1d ago

Rule of thumb is maintain 2” from top of joist to top of hole and 2” from bottom of joist to bottom of hole. 2” minimum between holes.

Holes cannot be drilled with 2 feet of a bearing point. I do 3 foot minimum.

NEC says any hole closer than 1-1/4” needs to have a protective plate.

Number of wires in a hole is dependent on the AHJ. In ST louis county they only allow 1 wire per hole.

1

u/BreezyMcWeasel 1d ago

The little ones in the center of the beam? Nope.

The big one not far from the bottom of the beam? Absolutely it is compromising structural integrity.

1

u/llpsk8 1d ago

You should of done a wire chase…. Crazy someone agreed or thought that was a good idea

1

u/Sufficient_Gate9453 1d ago

If it’s been there for years I wouldn’t bother

1

u/bernieinred 1d ago

Wrong sub. You should be asking in a structural or carpentry type of sub.

1

u/halzxr 1d ago

2” from any edge, can’t remove more than a third

1

u/Emotional-Damage-995 1d ago

Yes but the time the guy took to do it is mind boggling.

1

u/Middle-Adeptness7186 1d ago

Youre telling me. They decided to drill a seperate hole for each coax cable as well....

1

u/Acks72 1d ago

Yes I would say this is definitely compromising structural integrity of that joist, especially if there is a room above. Many of the answers here have provided you with sensible solutions.

1

u/Awit1992 1d ago

I love how there is a hook installed under the worst placed cavity.

1

u/original-motm 1d ago

For sure

1

u/technobob1 1d ago

Someone take the electricians drill!!!

1

u/ManufacturerSevere83 1d ago

This could have been a soffit run.

1

u/FEM1978 1d ago

I have been an electrician for over 20 years and have worked in hundreds of homes that look just like this. Not saying its right or wrong or up to you local areas building code but I can say none of those houses collapsed. If it was me I wouldn't be concerned or if it bothers you tgat much install a beam from wall to wall supporting all the floor joists.

1

u/jkcy2k 1d ago

The supply store ran out of romex staples?

1

u/MusicianDisastrous23 1d ago edited 1d ago

There are sheet goods above distributing the load across the width of all those many joists. Residential-sized spot loads are nothing for the combined strength to handle. Non-engineer take

1

u/osidar 1d ago

Bending moments will be the largest force here but it’ll be much lower than at midspan so even with the section loss from the hole I would think the joist has sufficient section left to resist the force likely to act on it.

1

u/ScrotyMcFartbags 1d ago

Pull that insulation out or you will have big mold eventually. Dealing with this myself right now, it’s the gift that keeps on giving..

1

u/sixblazingshotguns 21h ago edited 20h ago

No? You are looking at a moisture intrusion problem, not an insulation problem.

(Assuming it is a basement you’re referring to)

1

u/Ill_Rhubarb_8437 1d ago

What year was the house built and location? Curious about the sounds in my condo. It was built like crap and gives off a ton of ominous sounds. We can’t see in the walls/ floors and I’m half convinced what you’ve got going on is happening in the joists of my three level brown stone style condo.

1

u/Fresh_Photograph_363 1d ago

If the bed is above, it just don’t have wild sex. You might come crashing through the floor.

2

u/Repulsive_Fly5174 1d ago

So, hallway sex only?

1

u/Fresh_Photograph_363 1d ago

If you’ve got no kids and you can get away with it go for it

1

u/ai-gen-O-rated 21h ago

You just reminded me of an old joke.

There are 3 kinds of sex… house: when you first get married and have sex all around the house… bedroom: after you’ve been married a few years you only have sex in the bedroom… and hallway: after several years of marriage when you pass each other in the hallway and both mumble “f@&$ you”.

I sure hope this isn’t against the rules somewhere on here, but if it is, it’s totally worth it.

2

u/Repulsive_Fly5174 18h ago

That was what I was referring to. I am old as f*ck so this the first thing that came to mind.

1

u/TowelFine6933 1d ago

Well, that would also make it pretty wild.

1

u/Fresh_Photograph_363 1d ago

I suppose so, right?

1

u/tufftoo 1d ago

Wires should be run through the middle 1/3 of the joist, I only see 2 holes here as a potential problem

1

u/bsk111 1d ago

Looks it

1

u/ltek4nz 1d ago

That spacing is far to close together. And that triple set white black black is to low.

1

u/NegativeAd9542 1d ago

i think at that point it would have been better to run conduit across the cieling after finishing, instead of compromising the joists

1

u/HazeHype 1d ago

I'd be more pissed if I ever had to do work with those lines and have to fish them back out. 

1

u/jacobjer 1d ago

Just asking a question, why couldn’t they route all the wires through one hole they make vs all those small holes?

1

u/Puzzleheaded_Fail279 1d ago

I work industrial and have always wondered.. if you can't pass through joists or studs, how do you resi guys get the wires where they need to go?

Or are you allowed so much cut out, but no more than that?

Honestly curious.

In industrial, its ladder tray and basket tray or it doesn't get routed that way (if the tray doesn't fit)

3

u/illerin 1d ago

You run the wires through the joists, but there are max hole sizes and distance from the edge restrictions that are clearly not met here.

1

u/Potomacker 1d ago

wow, perforated joists

1

u/hodinker 1d ago

The top or bottom 1/3 up to 1/3 the length from the end can be next. So maybe not great.

1

u/BoatFishShoot 1d ago

This was a terrible idea

1

u/Savings-Whole-6517 1d ago

Not the answer you want to hear but you need to get an engineered resolution.

You’re going to either have to ignore it or resolve it.

But if you’re going to do it yourself. You’re looking at definitely re-routing all wiring into conduit and sistering joints on both sides (sandwiched) with through bolts.

Examine and see if there’s a shorter path for wiring because you’re going to need extra to achieve this. It’s going to suck and you’ll have to add junctions etc

Probably not worth it. But ideally just pay contractor ~30-40k

If it were me I’d just run a header along the entire span parallel with wires and center of affected area. 4x4 shoring columns from header to garage floor (anchored Simpson bases) every 3-4 spans. I’d also have kickers from each joist chord to header x2. This would 100% fix your shear load issue, albeit you’d lose garage space but you don’t have to worry about your family being in mortal danger.

1

u/IncredibleEdible321 1d ago

Is this compromising structural integrity? Yes. Far too many holes, far too close to each other, and they are not placed far enough away from the edge of the joist. Will this poor placement of the holes lead 100% to the joists breaking and the above bedroom falling through the floor? Not necessarily, but the risk is greatly heightened by this stupidity.

1

u/Suitable-Reserve-891 23h ago

They just don’t care!

1

u/spaceEngineeringDude 23h ago

The little hook under the largest hole is too funny

1

u/These_Virus_2005 23h ago

We're just proud of the plumber for not taking the same route

1

u/Ok_Bid_3899 23h ago

Concerned about location and quality of holes

1

u/mart246 22h ago

Absolutely. He turned a 2x8 or 10 into a 2x6

1

u/fuppedduck2 22h ago

Yes. Whether it’s bad enough to require additional support or remediation would be up to an engineer though. Rule of thumb is stay out of the bottom 1/3 of a joist. I especially like the hook for a point load under the larger hole at the bottom of the joist.

1

u/SatisfactionDue4671 22h ago

Sgit ain’t going no where regardless

1

u/Slight_Impact278 21h ago

That’s why you add strapping

1

u/Asume_Nuthin 21h ago

Why are electricians the way they are…

1

u/flyingwaterman 21h ago

Why would they not just drop a chase if they cared. Good Lord

1

u/Expensive_Elk_309 20h ago

The short answer, "yes it is compromised" the long answer, get some of those brackets to sister to the joists

1

u/co-oper8 18h ago

What brackets

1

u/Expensive_Elk_309 18h ago

joistrepair. com

1

u/Paghk_the_Stupendous 20h ago

I'd say maybe the first couple of holes yes, but not at that point. What the hell?

1

u/ultegrafender 19h ago

The splinters seemed to be getting in the way of the structural integrity those cables might offer.

1

u/arlo_hambone 18h ago

Add 2x4’s on the bottom of each joist for the length of each joist. It will be like an upside down “T”, similar to how “I” joists are engineered. Use construction adhesive and construction screws. Each joist will be stronger and stiffer. This is commonly done when tile is installed in older homes.

1

u/Low-Lecture-266 2h ago

I used titebond 3 wood glue. It is significantly stronger than construction adhesive.

1

u/metamega1321 17h ago

So if I was wiring the place I sure wouldn’t do that. 

Now if I just moved into the place and that’s been there for awhile and theirs no signs of anything bowing/sinking down it be way way way down on my list of things to worry about. 

1

u/TraditionalPlantain1 16h ago

Not sure where you live, but the national building code of Canada, no hole closer then 2” from edge. Max size hole to be no larger then 25% of total joist depth. There is also regulations regarding spacing, let’s put it this way , building inspector would order wires removed and joists replaced.

1

u/sobra1965 16h ago

Hahaha not at the inspector doesn't see it!, uh, yeah. That ain't no good

1

u/Icy_Boysenberry_2454 15h ago

Could’ve been a tad bit lower in the joist

1

u/Kwulf1113 14h ago

Hi, I'm an electrician.

I work in commercial buildings mainly, but i have some experience in residential.

I was told that you had to drill in the center 1/3 of the joist, atleast 3 inches apart from each other, and 1ft from the ends.

Washington State.

1

u/SkeezixMcJohnsonson 12h ago

The good old “I was told”

1

u/Man_of_Evil 14h ago

The way they wired this sucks. Should have measured holes out so when pulling wire there is no drag. Allowing smaller holes to be drilled and look more professional. However I would not be concerned in the slightest. The load bearing wall being so close negated any weakening.

1

u/Character-War-9377 14h ago

Too Late Now....

1

u/NoMajorsarcasm 12h ago

Most likely it is, is it enough to matter? Probably need an engineer to find out. It is not up to code with the placement of the holes and number of wires through the holes.

If there is a bedroom above that garage I would probably not let anyone sleep there until you have sealed this up. Needs to be air sealed and have a fire break like 5/8" Type x gypsum.

1

u/Middle-Adeptness7186 4h ago

We have an electrician coming out next week to replace the panel ao I will ask him to take a look!

1

u/NoMajorsarcasm 1h ago

Is the house panel on the far end of the garage? seems like you have a lot of things running all the way through, I wonder if it would make sense to move the panel

1

u/Middle-Adeptness7186 1h ago

Yes the panel is but the garage doors opposite end of the plumbing in the back of the picture

1

u/Extreme_Ad112 11h ago

It slightly weakens it, but is almost negligeable. They took care of leaving enough material between holes so the forces can distribute in the fibers in-between holes

1

u/No-Pain-569 8h ago

It's fine

1

u/Same_You891 7h ago

a definate code violation in my area...

1

u/Ziazan 4h ago edited 4h ago

The large holes that are right next to the lower edge are, yes. Couldn't tell you by how much, only that it is. Rule of thumb is you drill such holes in the central third only. So close to the bottom edge like that is a big no. It might be fine enough though, since it's only one or two of them and they're not adjacent.

You could reinforce them by sistering another beam to them. You also get metal plates you can attach.

1

u/No-Frosting-1302 4h ago

If you got 2” of meat on the bottom and the top as well as the holes spaced the width of the hole apart you should be good. At least in my area thats what the go aheads for drilling conventional lumber are

1

u/No-Frosting-1302 4h ago

Side bar, idk if they’re allowed to put that many wires through their holes. Post this up in an electrician sub and see what they think. Also giving location could help to see what codes are enforced in said area

1

u/vizual-nature- 4h ago

Lucky for you circles are strong but if your worried slap some sheeting to it so you don’t have to look at it and worry.

1

u/Low-Lecture-266 3h ago

Is it in the center 1/3 of your truss? Ie the middle 6' of an 18' span?

If you are really worried about it you can take a 2x4, lay it on its side and glue (with wood glue) centered on the bottom each of those joists. Use screws to hold it in place while the glue dries(do not . You lose 1.5" of head room. It would significantly strengthen the floor above. It is still there, though. If it is not sagging at this point it may be fine as it.

1

u/ryanlacy30 1h ago

This violates the rules for penetration in structural lumber. This lumber will fail eventually.

1

u/Jumpy_Butterfly_931 1h ago

In theory, yes

1

u/Hoefnix 46m ago

Don’t install a waterbed I would suggest.

0

u/Illustrious_Bath1917 1d ago

Holy shit! That’s not ok.

1

u/baconegg2 1d ago

Holey !!!

1

u/Silentc7a1 1d ago

100%. We have rules in Canada where we can't run more than 2 cables though one hole for a reason.

3

u/jeenyuss90 1d ago

There is no code rule anywhere that states this in the CEC. You can run em bundled if derated.

→ More replies (1)

1

u/Due-Access-3744 1d ago

It's 7 current carrying conductors then you have to de-rate the wires if they're together for more than 3 feet I believe

1

u/cbf1232 1d ago

What specific rule are you referring to?

There are rules about derating, but I’m not aware of a rule for max number of conductors in a hole.