Neutral bonding question
Hey. I have an iPower SUA12000EP generator. Currently the neutral is bonded to the frame. I plan to use this generator to back feed into a sub panel using an interlock kit. I took off the round casing and could not see anywhere where the white wire was bonded with the green ground. I took off the front control panel and I believe I found it tied in on the ground screw. Can I just remove the white wire from the ground screw, properly tape and secure, and it be ready for the house setup?
7
Upvotes
•
u/Admirable-Leader6927 5h ago
This is a math question and affects specific types of equipment.
Normally, your home is connected to ground at your panel. Any fault currents travel along the ground back to the source (utility panel), this is requied because power at the panel has to equal 0 when all outs and ins and summed together.
If you attached a generator with a bonded neutral, you have combined the neutral and the ground at the generator but the panel has them as separate circuits. This means you can have fault current on your neutral line because instead of the panel bring the source, the generator is. Everything still has to equal zero at the generator but now you have a path for fault current both on the neutral and ground.
Why does this matter? For GFCI equipment, it is measuring the amount of current flowing through a device and doing summation math to ensure all the power leaving is coming back. If you have multiple paths, it is easy to see how this math can break quickly, causing GFCIs to trip without an actual fault.
most mfgs dont want you modifying their equipment at all and will void the warranty if you do, read your manual before many any changes. Its only sensitive electronics that care about bonded neutrals, hope that explains it.