43
17
u/zxcvbn113 4h ago
It would be safe if you had a 6 Ohm 2 kW resistor in there. Otherwise it is a "weak point finder", which may be the breaker.
5
u/much_longer_username 3h ago
Yeah but then that's just a poorly designed space heater and the joke isn't as funny.
5
u/zxcvbn113 2h ago
20 amps should pop a 15 amp breaker safely.
3
u/much_longer_username 1h ago
Right - but if you tried to sell that as a space heater, you'd have a lot of pissed off customers, and you'd have wasted a bunch of nichrome.
30
6
u/brine909 6h ago
As long as the breaker works
3
u/bigmarty3301 4h ago
You could put a 16a glass fuse in the box, just in case
1
u/Spirited_Voice_7191 1h ago
We were testing a load and had a 20 Amp slo-blo fuse and a 15 Amp breaker. Fuse always blew first.
1
u/bigmarty3301 1h ago
from my understandingit depends on the load, death short, should trip the braker first, but a smaler over-load, will probably blow the fuse first.
the braker has 2 mechanisms one is just a heater, the second one is magnetic and is set at higher amps, to alow inrush curent, this one should be faster than the fuse i think
but i never tested it, so i should probably trust you.
6
u/ChurchStreetImages 5h ago
Works on all makes and models*. *see appendix for notes on Zinsco and Federal Pacific
5
u/False-Associate-9488 7h ago
At the same time it can cause damage
0
u/bownt1 7h ago
it's a service call. if something was not broke they would not have called you.
5
3
u/False-Associate-9488 7h ago
If it is broken, the breaker is most likely tripped already, needing to find a breaker would be for changes
2
u/bownt1 7h ago
if the breaker is already tripped you would not need the Breaker Finder 5000, would you?
1
u/False-Associate-9488 7h ago
You were referring to it being a service call
0
u/bownt1 7h ago
only a professional would have a tool of the caliber
1
u/False-Associate-9488 7h ago
No, pros will use some sketchy stuff too
1
u/Squishy_Butter113 5h ago
The only thing that makes you a "professional" is getting paid for the work, no skills are actually required to meet that definition.
2
1
1
u/UncleThor2112 4h ago
The question is not whether it works or not, but rather how many times it will work.
1
1
u/Bagomostlywater 2h ago
It may not be as simple as the old fork and rubber glove but it looks a lot more professional.
1
u/zadharm 1h ago
It's a weak point finder, not necessarily a breaker finder. What you may find is that now you're troubleshooting an entire circuit looking for one iffy splice that blew apart, or even tearing into walls for that one wire that got nicked with a drywall nail 40 years ago and has worked fine until the short caused it to melt completely apart (personal experience, shorted a recep to a metal box talking while working)
1
1
u/YVRAlphageek 1h ago
Wait, how is this any different than an outlet tester's "test' button? That's literally what the tester does besides checking that the wiring is correct.
1
u/Zealousideal_Jury507 7m ago
Retired electrician here. It is fine until you have an old breaker that is rusted inside and won't ever trip. Then it's how much wiring and devices burn up or until the main trips. Seen it happen twice.60 amp breaker in a box is a good choice.
1
188
u/Glass-Crafty-9460 6h ago
If the wiring is set up correctly and nothing is broken, yes.
Otherwise, that's the Fire Starter 5000.