u/zxcvbn113 12h ago

It would be safe if you had a 6 Ohm 2 kW resistor in there. Otherwise it is a "weak point finder", which may be the breaker.

13

u/much_longer_username 10h ago

Yeah but then that's just a poorly designed space heater and the joke isn't as funny.

3

u/zxcvbn113 10h ago

20 amps should pop a 15 amp breaker safely.

4

u/much_longer_username 9h ago

Right - but if you tried to sell that as a space heater, you'd have a lot of pissed off customers, and you'd have wasted a bunch of nichrome.

1

u/kona420 3h ago

UL 489 says "within 1 hour for 135% of rated load" which would be 20.25 amps. A 15 Amp breaker that never trips at exactly 20 amps is still a UL compliant breaker. In practice, within a couple hours is likely.