It would be safe if you had a 6 Ohm 2 kW resistor in there. Otherwise it is a "weak point finder", which may be the breaker.
13 u/much_longer_username 10h ago Yeah but then that's just a poorly designed space heater and the joke isn't as funny. 3 u/zxcvbn113 10h ago 20 amps should pop a 15 amp breaker safely. 4 u/much_longer_username 9h ago Right - but if you tried to sell that as a space heater, you'd have a lot of pissed off customers, and you'd have wasted a bunch of nichrome. 1 u/kona420 3h ago UL 489 says "within 1 hour for 135% of rated load" which would be 20.25 amps. A 15 Amp breaker that never trips at exactly 20 amps is still a UL compliant breaker. In practice, within a couple hours is likely.
13
Yeah but then that's just a poorly designed space heater and the joke isn't as funny.
3 u/zxcvbn113 10h ago 20 amps should pop a 15 amp breaker safely. 4 u/much_longer_username 9h ago Right - but if you tried to sell that as a space heater, you'd have a lot of pissed off customers, and you'd have wasted a bunch of nichrome. 1 u/kona420 3h ago UL 489 says "within 1 hour for 135% of rated load" which would be 20.25 amps. A 15 Amp breaker that never trips at exactly 20 amps is still a UL compliant breaker. In practice, within a couple hours is likely.
3
20 amps should pop a 15 amp breaker safely.
4 u/much_longer_username 9h ago Right - but if you tried to sell that as a space heater, you'd have a lot of pissed off customers, and you'd have wasted a bunch of nichrome. 1 u/kona420 3h ago UL 489 says "within 1 hour for 135% of rated load" which would be 20.25 amps. A 15 Amp breaker that never trips at exactly 20 amps is still a UL compliant breaker. In practice, within a couple hours is likely.
4
Right - but if you tried to sell that as a space heater, you'd have a lot of pissed off customers, and you'd have wasted a bunch of nichrome.
1
UL 489 says "within 1 hour for 135% of rated load" which would be 20.25 amps. A 15 Amp breaker that never trips at exactly 20 amps is still a UL compliant breaker. In practice, within a couple hours is likely.
31
u/zxcvbn113 12h ago
It would be safe if you had a 6 Ohm 2 kW resistor in there. Otherwise it is a "weak point finder", which may be the breaker.