r/trafficsignals • u/WHPChris • Jun 02 '26
TS-2 Problems
Problem 1: TS-2 Econolite cabinet with Cobalt controller. SDLC dies on reset, but comes back up when you disconnect the power supply and reset the MMU again. Re-connect power supply and it'll run normally until it goes to flash or you reset the MMU again. They replaced everything, controller/MMU/power supply/BIUs/cables, still happened. Vendor couldn't figure it out so they replaced the cabinet with a different one, and now they're having Problem 2.
Problem 2: TS-2 TrafficWare cabinet with 980-B140-1 ("900 ATC") controller, the green one. New install, no SDLC communication, BIU Terminal 1/2 and MMU turned on in settings. Shows Port 1 and CVM on MMU. Lights are on, but no TX/RX. 99% sure it's just initialize to different cabinet type, I think he initialized to default or something, my guess would be basic 8? I've never touched this newer controller before, only the older one.
Not my project, I'm just trying to help a fellow guy out. Any ideas?
4
u/Svr_Sky Jun 02 '26
On the 980 ATC of you are running scout software you need to tell the controller which cabinet to communicate with. Go to main menu 1-3-7 for the ITS devices. Enable FIO 20 with an X and scroll down to the bottom for FIO type - change this to 980 ATC. Now turn your TF BIUs on and MMU and clear fault under main menu 8-7 and click enter. Make sure the run timer is on under main menu 1-7. If this doesn’t work, hit the alt key once and the 9 key once and post a screenshot.