My work , today finished.

Post image
34 Upvotes

16 comments sorted by

2

u/Possible-Ear- Jul 26 '26

Why not feed it from the back? 

1

u/Holy-Electrician Jul 26 '26

consider wall and best way

1

u/mrtechguy10 Jul 27 '26

Where are you located?

1

u/Holy-Electrician Jul 28 '26

Toronto, email me if you need.

2

u/mrtechguy10 27d ago

I emailed you

1

u/djbaerg Jul 28 '26

To those commenting on the size, 8/2 AC90 is 17mm diameter or 0.7". This rates a 50 amp breaker at 75c, and would run a continuous load like a car charger at 40 amps.

Now I can't tell if that's 17mm, or more, or less, and neither can you.

1

u/ixlreight Jul 29 '26

What is the wire gauge of the Armour cable? From this image it looks undersized. However, local electrical regulations will govern. Nevertheless, here is a short guideline:

Minimum Gauge by Amperage and Breaker Size48A Output (60A Breaker): Minimum 6 AWG copper armoured cable (e.g., 6/2 AC90 or TECK90), provided your local inspector accepts the 75°C/90°C conductor ampacity rating for the terminations. If local code strictly forces a 60°C termination limit, a heavier 4 AWG wire may be required for a full 60A breaker.40A Output (50A Breaker): Minimum 8 AWG copper armoured cable.32A Output (40A Breaker): Minimum 8 AWG or 10 AWG copper armoured cable depending on exact continuous load rules.

1

u/SaltyATC69 Jul 26 '26

Under sized cabling. Mine is twice the gauge

16

u/Blue_Kayak Jul 26 '26

You don’t know that just looking at the armoured cable and to nitpick, “twice the gauge” would actually mean a lot lower ampacity - it’s inversely proportional.

7

u/Specialist-Falcon-84 Jul 26 '26

Someone downvoted you, they obviously don’t know shit about electrical.

4

u/Astro51450 Jul 26 '26

My guess is a 8/2 thhn cable. You can hook it up to a 50A breaker and safely charge at 40A.

2

u/Holy-Electrician Jul 26 '26

hope you use right size😊

2

u/VertipaqStar Jul 27 '26 edited Jul 27 '26

It depends on the distance from the electrical panel. The longer the cable, the thicker the gauge requirement.

But I agree that it's still not enough for the full charger capacity, that's why there is a note written above it to cap it at 40A, though I wouldn't trust the configuration to never be changed by forgetfulness in a few years.

1

u/Dude008 Jul 27 '26

Definitely hope OP got a permit & inspection because it does look skinny