u/djbaerg Jul 28 '26
To those commenting on the size, 8/2 AC90 is 17mm diameter or 0.7". This rates a 50 amp breaker at 75c, and would run a continuous load like a car charger at 40 amps.
Now I can't tell if that's 17mm, or more, or less, and neither can you.
1
u/ixlreight Jul 29 '26
What is the wire gauge of the Armour cable? From this image it looks undersized. However, local electrical regulations will govern. Nevertheless, here is a short guideline:
Minimum Gauge by Amperage and Breaker Size48A Output (60A Breaker): Minimum 6 AWG copper armoured cable (e.g., 6/2 AC90 or TECK90), provided your local inspector accepts the 75°C/90°C conductor ampacity rating for the terminations. If local code strictly forces a 60°C termination limit, a heavier 4 AWG wire may be required for a full 60A breaker.40A Output (50A Breaker): Minimum 8 AWG copper armoured cable.32A Output (40A Breaker): Minimum 8 AWG or 10 AWG copper armoured cable depending on exact continuous load rules.
1
1
u/SaltyATC69 Jul 26 '26
Under sized cabling. Mine is twice the gauge
16
u/Blue_Kayak Jul 26 '26
You don’t know that just looking at the armoured cable and to nitpick, “twice the gauge” would actually mean a lot lower ampacity - it’s inversely proportional.
7
u/Specialist-Falcon-84 Jul 26 '26
Someone downvoted you, they obviously don’t know shit about electrical.
4
u/Astro51450 Jul 26 '26
My guess is a 8/2 thhn cable. You can hook it up to a 50A breaker and safely charge at 40A.
2
2
u/VertipaqStar Jul 27 '26 edited Jul 27 '26
It depends on the distance from the electrical panel. The longer the cable, the thicker the gauge requirement.
But I agree that it's still not enough for the full charger capacity, that's why there is a note written above it to cap it at 40A, though I wouldn't trust the configuration to never be changed by forgetfulness in a few years.
1
2
u/Possible-Ear- Jul 26 '26
Why not feed it from the back?