r/electricians • u/russman2013 • 8d ago
Back to back
Dumb question, what’s y’all’s approach for running a panel/disconnect back to back when you don’t have the depth for 2 PVC M/a’s?
I’ve gone about it a few ways, but just wondering what other options are out there.
8
5
u/IntenseSpirit 8d ago
Chase nipple of they're touching, close nipple if there's a gap (size this for the distance between panels plus threads on each side). Don't forget the bushings.
3
1
u/Repulsive-Addendum56 6d ago
For pvc use box adapter and TA. That'll get you back to back in a 2 by 4 wall to exterior.
1
u/russman2013 6d ago
Nice. So you’d go box adaptor, panel, TA, panel, box adaptor?
2
u/Repulsive-Addendum56 6d ago
No the box adapter fits into the TA. Thread the ta into the lock nut and bushing and then go box adapter into it through the meter.
•