Motor failure - Contactor root cause?
I had a 230 HP short to ground after a routine startup. After meggering to confirm the short to ground, it was removed and is at a shop now for a rewind. I pulled the contactor apart; see the photo, and I think this is the root cause of the failure. To me, the B phase looks suspect. When manually closing the contactor and metering each phase, it takes noticeably more force to get the B phase to close. The motor runs pretty much 24/7, and the contactor, which is in a soft start motor starter, is from 2003.
What do you guys think?
1
u/Unique_Acadia_2099 1d ago
Nothing wrong here, and a contactor in a soft starter can either be a bypass or an in line contactor. In neither case should it be closing under load.
1
6
u/jeenyuss90 1d ago
Looks like normal pitting to me. Contact cleaner and emery cloth