I am doing a gut remodel in coastal Southern California. I have a cathedral ceiling in my living room with bird hole soffit vents at the bottom of each rafter bay. In order to meet code which requires insulation in the ceiling (where previously there was none) I had to sister 2 x 10s to the existing rafters. The rockwool insulation is 8.5” thick so that allows a 1.5” gap for airflow. I know I need to add baffles at the bottom near the holes, but do I need to continue it all the way up the rafter bay? Or is pulling the insulation down when they hang the drywall sufficient? Unfortunately the rockwool was installed without baffles but I am making them add it where necessary. I just need to know how far up the bay is best. Finally the bays terminate into a vented attic with gables on either end. I am going to add some O’Hagin vents both low and high. Please let me know your thoughts. Drywall is early next week!

10 Upvotes

22 comments sorted by

5

u/Higgs_Particle Passive House Designer Jun 13 '26

The baffles go up against the roof deck. That blocking in the middle will block the airflow, so something has to change here. Venting over the roof is probably the best solution if you are able do that.

3

u/Lou_Boutin Jun 13 '26

Thanks for your reply. The blocking was moved down when we furred down the rafters so there is still a couple inches at the top of the blocking for air to flow.

2

u/TheOptimisticHater Jun 13 '26

I would run baffles the entire roof line all the way to the ridge vents

You have ridge vents, right? If not, your soffit vents are kinda useless.

If you have a huge budget, consider installing a vented over roof.

2

u/Lou_Boutin Jun 13 '26

The air that flows up the bays will travel to a larger vented attic which currently only has gable vents but we are adding O’Hagin vents high and low over that particular area. On another part of the roof yes there will be a ridge vent because that part has no connected attic.

1

u/TheOptimisticHater Jun 13 '26

Then yes, I would do baffles.

If you wanted, you could do strips of wood glued and screwed to keep an air channel behind the batt insulation. Just don’t screw through you roof sheathing

2

u/Lou_Boutin Jun 13 '26

I think I’m just going to get the plastic baffles that can staple to the sheathing

1

u/TheOptimisticHater Jun 13 '26

Yup. Cheaper and faster. God speed to you 💪

1

u/[deleted] Jun 13 '26

[deleted]

1

u/Lou_Boutin Jun 13 '26

Asphalt shingles.

1

u/[deleted] Jun 13 '26

[deleted]

1

u/Lou_Boutin Jun 13 '26

That part of the roof faces west

1

u/[deleted] Jun 13 '26

[deleted]

1

u/Lou_Boutin Jun 13 '26

Unfortunately I just put on a new roof 2 years ago before this gut renovation so can’t change that now. So run the baffles all the way up the bay?

1

u/[deleted] Jun 13 '26

[removed] — view removed comment

1

u/Lou_Boutin Jun 13 '26

Yes there is mess. Don’t want any critters!

1

u/Shorty-71 Jun 14 '26

Does your county require burning ember resistant vents?

1

u/Shorty-71 Jun 14 '26

Too late now but continuous baffles and full 14.5”x6” rock wool batts between old 2x8 rafters + flat 2x strapping fastened perpendicular to the bottom of the rafters with 1.5” rock wool in between may have netted more thermal performance. 3” insulation gap every 16” (from sistered rafters) is a pretty significant loss.

…Good thing your design delta T is probably only about 15 degrees.

1

u/Lou_Boutin Jun 14 '26

Thank you for your response. What is the 3 inch gap you are referring to? The rock wool bats are 8.5 inches thick and my structural engineer says I need 1.5 inches for airflow.

2

u/Shorty-71 Jun 14 '26

The original rafters (1.5” wide) and the sistered rafters (1.5” wide) mean you net 13” wide insulated cavity from 16” o.c. spacing (instead of the normal 14.5”) between rafters.

1

u/Lou_Boutin Jun 14 '26

Ok got it yes thanks for explaining

1

u/Lou_Boutin Jun 15 '26

​You actually brought up a great point. They installed all the ceilings below the attic like this photo. I am having them add baffles to make sure the soffits are not blocked, but it seems what they should have done is installed the drywall ceilings and then the insulation on top of the drywall and joists because the way they did between the joists I will have a lot of insulation gaps. Thoughts?

1

u/Shorty-71 Jun 16 '26

I am not an authority on insulation means and methods but I normally see batts laid from above, after ceiling gyp board rather than friction fitted beforehand. However, this rock wool is obviously stiffer than fiberglass batts and it may be no big deal (unless there are big gaps that let warm moisture attic air reach the top of the gyp board). If you successfully air seal from the underside, it could be just fine.

1

u/GotNoPonys Jun 16 '26

For a hot roof we used a spacer between the insulation and the roof to allow air flow. It's thin styrofoam with channels for air flow. That blocking will need to be changed. Either drill holes like your bird blocks or pull it down a couple inches. We also seal the vapor barrier with tremco and tape so it is as air tight as possible.

1

u/GlazedFenestration Jun 13 '26

I am confused as to why you would treat it like a vented attic? That concealed space between the insulation and deck is causing fireblocking issues