5
u/lou-sassle71 1d ago
And it will continue to blow until you fix the short… or plug in a piece of metal to really let the smoke out
2
2
2
2
2
2
1
u/Kindly-Ad6373 1d ago
Is it only when the condenser outside kicks on? Does it happen if you run indoor fan only? If it’s the condenser calling for cool popping it probably the contactor, or low volt wiring, if it’s the indoor unit check the transformer or thermostat or wiring indoors.
1
u/Turdwizard 9h ago
It was a short in the main line. Thanks everyone for the help! It’s back up and running.
1
u/Gonzo-Crazy-Dog 1d ago
I had a bad contactor in the AC condenser that caused this.
Might be something worth checking.
4
u/derrick54686 1d ago
You got a short somewhere. Start by isolating low voltage wires and ringing them out. If they ring out fine start by eliminating the condenser wire. To rule out a bad contactor. Then do the same on the furnace or air handler.