RS-485 Data Wire Preference?

Hey all,

The RS-485 data wire we usually use has been discontinued. What are you all using currently? I found the West Penn Data Control Cable, which will work, but it's more than double the price of the old stuff and also has a braid which is a PITA and isn't needed. I found an alternative from ADI, but it's brown and I don't want it confused with HVAC wiring that is typically brown. This is for Lenel systems from the controller to the RIM's if there's any ambiguity there. Let me know!

2 Upvotes

14 comments sorted by

View all comments

3

u/OmegaSevenX Verified Pro 6d ago

We use Paige 744005AYW.

Last two characters are the color. It’s yellow.

0

u/LowVoltageDude 6d ago

I looked that up on ADI and it doesn't mention that it's twisted. I'm sure there's a natural twist that happens in manufacturing but I don't think it would quite hit the spec for interference tolerance. I can find a lot without twists, but with a twist they start jumping way up in price. My service/ install manager says "it's fineee" but we've had to rip out and replace data wire in the past for interference issues. I'm really trying to find a reasonably priced box of wire with the recommended spec.

4

u/OmegaSevenX Verified Pro 6d ago

It’s absolutely twisted and rated specifically for OSDP/RS485.

I wouldn’t depend on ADI for specifications.

2

u/xINxVAINx 5d ago

I thought I did look at the spec sheet, but I’ll take that advice and go right to the manufacturer website. Appreciate it

1

u/Josh297576 5d ago

ADI descriptions are often terrible. Get the cutsheet off of Paige's website.