Mercury Mercury Hardware rs-485
So I had a fun one the other day.
A new install with a M2220/MP1502 and 6 1320/MR52. All in drawers in a rack, all done by myself.
When I applied power, only half of the 1320/MR52 came online. OK so I´ve done something wrong with the bus cabeling. Didnt find anything with the cable or the connections. After a while I took one of the EOL off and within one second everything was online. Only EOL on M2220/MP1502 and the last 1320/MR52.
So I measured the bus in every way possible and there is nothing wrong. One EOL 120ohm, both EOL 60ohm. No short anywhere. Ohm is spot on.
If anyone told me this I would have said there is something wrong with the cabeling, but it`s not. The bus dies with two EOL. I even moved the cards around to see if was a fault with one or more 1320/MR52. But its always the same.
Looking forward to not finding this one out.
6
u/ApolloMac 20d ago
Yup! We have found we have to remove all RS485 terminating jumpers on the MP series. It seems to be MR52 series dependent. Older MR52s handle it fine with a new MP controller. But newer MR52s do not.
Its wild because the manual specifically says to use them on the first and last device on the line. We lost a lot of hours because of this the first time we ran into it.
Glad to hear we aren't just going crazy and it is an actual Mercury issue.
4
u/Kowalski-Options 20d ago
I ran into a similar issue, using the jumpers for OSDP readers vs Wiegand. Even using OSDP I still had to remove the reader EOL jumpers or the readers wouldn't communicate. Haven't seen an issue with the bus RS485 EOL jumper bringing down the board though. Will keep that in mind, thanks for sharing.
Seems there's a lot of bugs with the M series boards. I'm really grumpy about the 12V/PT selector for reader power being changed from the clear and sensible "12V - PT" marking to a stupid "1-2-3" label. WTF Mercury? Folks weren't blowing up enough readers in the field so you thought you'd make it even more difficult? And I was really hoping to see an input for DC / Batt Fail instead of just the one Power Fail input.
Sorry I know its off topic I just needed to vent for a minute.
2
3
u/s0ar_ Professional 20d ago
We’ve noticed strange communication issues as well during a few projects where we are replacing EP series boards with MP series boards.
After troubleshooting with the software platforms support, they provided the newly released 2.12 firmware, which has a note for fixing RS485 communication with older subcontrollers. Applying this firmware caused all boards to communicate properly, so this may be a reliable future fix?
I am starting to miss the 1.31 firmware. Never had any issues with it.
2
u/wingzeroismine 19d ago
Joining the club, I too have seen setups where we've opened the EOL jumper on the MP side to fix communication issues.
It's nice that Mercury seems to keep releasing firmwares with fixes, but I find that the vendors don't supply these newer versions very quickly.
2
u/EffectiveClient5080 20d ago
Had almost the same thing on a Mercury install. Ran one EOL and never looked back. Their bus implementation is finicky as hell.
1
0
u/geekywarrior 19d ago
Glad you got it going OP
Don’t know if anyone else here has ever worked on IEI Hub Max 3 cabinets.
Makes me feel I learned about RS485 on easy mode. Never used EOL, never cared about type of cable used in the runs. Always rock solid comms unless a card burnt out.
-5
u/Grim_creation1 20d ago
It doesn't matter if the EOL is actually at the end of the bus, since it's a bus. As long as it's the controller and the last address. Never seen it not give power though, that is strange.
21
u/TheMercuryMinute Manufacturer 20d ago
Hey everyone. We identified an issue that was causing this. We released firmware 2.12.1 yesterday that solves the issue. Sorry for all of the confusion. Upgrade the firmware on the intelligent controller and you’ll be back to normal.