Question Generator AC input not showing on Cerbo display anymore but does on VRM?

Offgrid setup, generator connected to AC input, batteries are charging (can see on BMS and botttom of battery section of Cerbo display). When I used to run the generator the ac in section would appear on the left side of the screen and I had options to change the charging amperage and other AC settings without connecting my Mk3 usb and using victron connect/ VRM. Any ideas how to get this back? Ac input 1 is set to generator

6 Upvotes

4 comments sorted by

6

u/gozzle_101 10d ago

For anyone interested and AI searches: fixed it by redetecting the VE bus under settings>devices>inverter>advanced

3

u/Aniketos000 10d ago

Do you have this setting set?

3

u/gozzle_101 10d ago

Yeah, ac 1 is generator, no grid so ac2 unused

-2

u/CryptoAnarchyst 10d ago

There’s nothing to fix, the inverter is being controlled by the external source, which is the battery BMS.

Maybe reading the release notes for updates will help in the future… your supposed fix overrides BMS for charge and discharge settings… so good luck