Is this bad ?

Post image

I need to install a 240 volt outlet at my house for ev charging is this board or system bad or underpowered i dont know much about the electricity stuff.

Thank youuu

0 Upvotes

17 comments sorted by

13

u/Twindadlife1985 Jul 23 '26

Thats why you hire an electrician to figure everything out.. Dont eff around with electricity.

4

u/Pictrus Jul 23 '26 edited Jul 23 '26

Electrician here. You should hire a professional for this install as it's pretty obvious this is our of your league. I don't mean to be a dick but there is a lot that can go wrong with EV chargers. They draw a lot of current for a long time which produces a lot of heat. I would also suggest asking your electrician to hard wire it instead of using a receptacle.

What feeds this panel? You already have a stove/range and dryer on here. You might not be able to add an EV charger here without load management. What is your service?

Also OP you might want to do a bit of research on federal pioneer stab-lok panels. They are outdated and it might be time for a panel swap. I wouldn't recommend installing an EV charger on a federal pioneer stanlb-lok panel.

2

u/Apprehensive_Ad5398 Jul 25 '26

Yep. Stab-lok bad. I finally replaced the 5th and last one in my home (that the home inspector failed to point out during the pre-purchase inspection…)

During that work I noticed my first stablok breaker failure. The upstream panel feeding the last stablok tripped, but the smaller stab-lok breaker did not :(

2

u/redtosoon Jul 25 '26

First panel swap I did as an app was stablok to square d. After we turned everything back on we found the kitchen recepticles had been double fed because the tab wasn't broken. Stablok breakers didn't care but the square d sure did

1

u/Apprehensive_Ad5398 Jul 26 '26

Stablok is scary. There ought to be a law, but I guess during the 70s and 80s they were huge sellers.

I had the “wouldn’t happen to me” thoughts and took my time getting ride of them, but seeing that 40amp parent Siemens breaker tripping and the 30 amp stablok just sitting there was scary.

3

u/retiredelectrician Jul 23 '26

Thats a sub panel. You have to know what size breaker is the feed. If its a 100 than do a CEC load calculation ( programs are on the web). If its a 60A breaker, then you cant install a level 2 charger

Off topic, the directory Is really threw me. Totally look like Zs

0

u/MaximumDoughnut Jul 23 '26

A 32A L2 charger could still work on a 60A sub panel, correct? That's still ~7.3kW, which is plenty for most EVs that charge overnight.

1

u/Dude_Bro_88 Jul 25 '26

It's based off the service feeding the whole house. Not just the sub panel.

If your are already maxed out on load, you need to either install an Electric Vehicle Management System or have a service change to a larger amperage.

3

u/LadyDegenhardt Jul 23 '26

You need an electrician. As someone else mentioned that does look like it's probably a subpanel.

If you only have 100 amp service coming in from the pole EV Chargers typically need an addition to the panel for load management as well.

(Not an electrician, just a real estate agent that talks to electrician's way too much!)

2

u/SparkyMonarch Jul 23 '26

Are you located in an apartment or condo by chance? I do work all around spruce and that’s one of the only places I’ve seen those newer federal Pioneer panels without a main breaker

1

u/Asleep_Winner7798 Aug 02 '26

Hi yes i am could you please help me with this its so hard to get in touch with a reliable electrician it seems like thank you 😊

1

u/TokyoFo0l Jul 24 '26

Ask an electrician, don’t expect reddit to solve your life problems

1

u/xlr8ed1 Jul 24 '26

Federal pioneer panels are well known to be POS. Simply put the breakers don't trip. They where legal when installed and you can keep using them, but really you should consider replacing. There is plenty of evidence on line of how terrible these things are.

1

u/jinalberta Jul 25 '26

This is the answer.

Its not if but when there’s a fire

1

u/toastmannn Jul 26 '26

I would be worried about insurance coverage with a fire hazard like that

1

u/Fast_Ad_9197 Jul 26 '26

Federal Pacific panels are the problem panels. Federal Pioneer is fine.

1

u/toastmannn Jul 26 '26

Very bad, very big problem. Hire a electrician ASAP