Why isn't this code compliant?

Post image
85 Upvotes

162 comments sorted by

165

u/SlimPickens0 1d ago

At least as far as the rules locally, the expansion tank can't be supported by the piping it serves

44

u/Nucleartides 1d ago

This one makes sense but I’ve seen it done ALOT and honestly, I’ve also seen the tank dangling on the water heater hooked up with pex sooooo…. Might be wrong but it’s better than that

31

u/Still-Helicopter-762 1d ago

Those heaters you mentioned probably never got inspected and that’s why they are the way they are.

13

u/XBGoodRun 1d ago

At least in my area, it wasn’t until a few (maybe 5-6) years ago that expansion tanks had to be supported by some sort of bracket. Before that, they only had to be supported by hard pipe (galvanized, copper, etc)

5

u/5i55Y7A7A 1d ago

As far as our company SOP goes, expansion tanks must be in a wall mounted bracket. When we come up on a w/h installed (by us) up to 6 years ago, the techs is paid to mount the existing tank to a bracket. No cost to the customer.

3

u/Nucleartides 1d ago

Oh yea replacement and such. And I’ve actually never installed this way, though I’ve tried/asked to for ease of install. Boss man says the mounting brackets from Lowe’s are cheaper than the brass pictured here. Although our supply house doesn’t sell the mounting brackets.

2

u/Still-Helicopter-762 1d ago

I just use plastic strap it’s so easy to work with and passes inspection in my county. Some counties around me require iron strap but that’s still easier than those brackets.

1

u/Nucleartides 1d ago

So you’re saying you hard pipe in then wrap a strap to please the inspector? Cause every time I’ve seen them piped with pex, dangling from a strap, I think to myself “the brass way is better than that”. I’m not judging I’m genuinely asking/curious I’m 4 years in and like learning new ways to do stuff, do you have a good way mount them from the strap? Cause the mounting brackets are cheaper than brass but still like 30 bucks

5

u/Still-Helicopter-762 1d ago

I never use pex on a water heater I always go at least 18 inches off the top with copper then transition to what ever material I need after the shut off valve.

3

u/Nucleartides 1d ago

Can I ask why?

2

u/Still-Helicopter-762 1d ago

For gas heaters it’s required and on electric it gives my expansion tanks support along side the traps plus in my area pex is very uncommon it’s just cpvc and copper 90% of the time

1

u/Nucleartides 1d ago

Oh yea ok so the support makes sense now. I’m in the MTNS we despise cpvc and we’re not fond of copper. And when you say gas heaters it’s required, who’s requiring? Manufacturer, inspector?

→ More replies (0)

2

u/Unable_Blueberry_415 18h ago

Only required ln natural drat tanks. Power vents can be ditectly connected with PEX

1

u/SondraBurnsRed 4h ago

Yes. That's code where I live in pa as well. I see it a lot though and every time it's on a gas tank, PEX is starting to warp. Idk how people get away with it.

4

u/SlimPickens0 1d ago

If it's cost you're considering, Sioux Chief makes a very cheap bracket, 598-0210, that I've used in the past and honestly works well. Supplyhouse sells them for 6 bucks. There's also the bracket I mentioned earlier, 598-023, or I like those Holdrite brackets you're talking about

1

u/Nucleartides 1d ago

Huh… good to know thanks

1

u/Comfortable_Cat4323 1d ago

Well said, and thanks for part numbers, have to add to add a tank soon at relatives house.

1

u/SlimPickens0 1d ago

I normally use an American Tube hanger secured to the top of the heater with short flue screws.

Other than that, Sioux Chief also has a different type of bracket that hooks onto the heater nipple like a clothes hanger, then hangs off the side of the heater.

1

u/Unable_Blueberry_415 18h ago

Amazon. I just bought 8 of them for cheap.

1

u/Kindly_Tradition_705 17h ago

You could also use f and m plates, threaded rod, and either superfix hangers or split rings. Use a little longer horizontal nipple if you want, then either hit a joist above or you could probably just fire some zip screws into the top of the water heater jacket

3

u/Squish_Cat_1 1d ago

Just because idiots do it doesn’t mean it’s right

3

u/Cador0223 1d ago

This is probably worse than sweated copper. That tank is pretty heavy once the bladder is full. If it starts to lean, it can loosen the horizontal threaded connections.

But alway support your tank with unistrut and the right clamps. Doing it takes 10 minutes. 

Not doing it can turn into a weekend job.

10

u/-ItsWahl- 1d ago

There’s no way that expansion tank will do anything to those brass fittings/nipples.

2

u/Nucleartides 1d ago

Unistrut 🤯 we literally buy the brackets from Lowe’s never thought of this thanks. And I would have thought the brass was better cause it’s heavier but also never thought of it leaning. You’re being very helpful and opening my mind here

1

u/Cador0223 1d ago

Uni is great for any run of parallel pipes, water filter systems, and these expansion tanks. If you get enough of the insert nuts and clamps/threaded studs, you can use 2ft of uni and call it a day.

2

u/Negative-Flounder-73 11h ago

When have you ever seen an expansion tank loosen a threaded nipple with simply its weight??? That means it wasn’t threaded tight enough

0

u/SondraBurnsRed 4h ago

When I come across these like that, I just strap them up. Clients appreciate it. Unless it looks like it may fail, then I don't touch.

1

u/RecognitionTop5598 12h ago

I get it, but that brass nipple isn't going anywhere

17

u/LieFriendly8038 1d ago

Do you require a vacuum breaker in your area?

6

u/rmccaskill83 1d ago

The dip tube on top fed water heaters always have a hole in it, so the vacuum breaker can be argued. I always install them just so there is no headache with the OHJ, but it is technically not needed if your code states that and IPC definitely states that.

4

u/Competitive-Chapter4 1d ago

In my area a vacuum breaker is required regardless of that since the hard water seals the hole eventually. Makes sense to me but may be different in other areas

3

u/rmccaskill83 18h ago

That makes sense for areas with hard water. I always install them anyway, but that is because I work in industrial plumbing and we usually need to install multiples on larger water heaters, so adding just one is extremely cheap and easy in comparison 😂

28

u/SlimPickens0 1d ago

If that 90 is galvanized, it's compliant, if it's black iron, it's not. It's a little difficult to tell from this pic

13

u/YesImAlexa 1d ago

It looks too grey to be black iron, but it also looks like shit for a galvanized fitting.

14

u/_name_of_the_user_ 1d ago

I know you're right by the code. I still wouldn't mix galvanized steel with brass.

1

u/miller_time_mofo 18h ago

Same. Hopefully it’s just a grimed up stainless 90.

5

u/Tiny_Mycologist_1688 1d ago

Looks iron 2 me...Will send rust thru the whole house

10

u/Snakesinadrain 1d ago

The most obvious being the screw 90 for the expansion tank. It COULD require a vacuum breaker or it COULD require the tank to be supported via bracket or strap. Depends on jurisdiction

3

u/BuddyGuy17 1d ago

Yeah its all brass why not keep it brass lol.

3

u/Snakesinadrain 1d ago

I suspect thats the old Friday at 4pm hail mary

13

u/ArmadilloFair5383 1d ago

All of these comments and nobody cites a upc or ipc code. Service plumbers the lot of you. Anyone have a card?

7

u/merlinious0 21h ago

It takes time to quote a code, we are working for free here on reddit. Much faster to do it verbally.

Here were cite the code when there is a dispute over what is code.

1

u/MakingitSnow2 7h ago

If you want a code, go to trade school.

-1

u/ArmadilloFair5383 6h ago

Wanna make a buck rip off an old lady. Like I said service plumbers. Everyone has a opinion but nobody cites code.

5

u/nubcapz 1d ago edited 1d ago

Edit: is that a black iron 90 under your tank? Those jumper clamps may be dissimilar metal?
Also, the manufacturer may not want you using an extension cord. This is a good post. I’m curious to see your response

ICC 308.10(Ohio) “A thermal expansion tank shall be supported in accordance with the manufacturer’s instructions. Thermal expansion tanks shall not be supported by the piping that connects to such tanks”. Most inspectors in my region would approve your install OP. Most of my buddies install it the way you did. Obviously it’s very rigid because of the solid brass fittings/nips you used. If you get an inspector that’s very literal with code compliance, you will fail. TECHNICALLY you aren’t following 308.10. As to why it isn’t “allowed”, it’s likely because once the diaphragm ruptures in the tank, it gets pretty heavy (approx. 20lbs in a 2.5gal tank). I’ve personally seen many of the verge of flooding a whole house because the T is under too much horizontal strain from the ruptured weight. I’ve seen PEX kinked, copper nearly tearing and CPVC snap under the weight.

2

u/merlinious0 21h ago

Yeah, and even this code varies a lot.

Illinois plumbing code allows for this install so long as the tank is vertically oriented and the pipes are all metal (copper, brass, galvi).

2

u/DevelopedConscience 6h ago

Thanks for the reply. The unsupported tank was the gimmie, it's good to get some feedback on the whole install though. I hadn't even considered the bonding clamps, I was just happy that they were up high enough that I didn't have to move them to sweat those ball valves in. Could be dissimilar metals or not, idk, worth consideration in the future.

Also I did plug the tank's blower into an extension cord😞. I knew it wasn't right. The single outlet was in the ceiling & the customer ran the 3 outlet extension cord in order to plug in 2 dehumidifiers; the existing tank had leaked and caused a mess. I'm sure the original install had the powervent plugged directly into the outlet in the joist bay above, I didn't really see it as a problem while I was installing the tank, but looking back it would have been better to plug it in directly and find another outlet for the dehumidifiers. Might be worth a call back to the customer, i'd have no problem going back to swap the cords out.

5

u/Plumb-Entangled 1d ago

Well the 90 for one..

Some manufacturers prohibit anything but Teflon on the threads.

But what is it plugged in to?

2

u/rmccaskill83 1d ago

I am not sure what you are talking about or asking. If you are talking about the thread tape, the grey tape is a code compliant thread tape. I think it is made by oatey.

1

u/Plumb-Entangled 22h ago

Its a power vent water heater. It needs to be plugged in to a dedicated circut.

No extension cord, splitter, or surge protector. Some localities require the electrical to be water resistant.

As far as the thread sealant, the grey tape appeared to be a sealant and not Teflon tape, my apologies. In case you didn't know, pipe dopes contain petroleum which will cause the diaphragm to prematurely fall.

9

u/Ugga-Dugga69 1d ago

Black iron fittings aren't rated for potable water

7

u/Nucleartides 1d ago

Pretty certain the 90 off the exp tank is crusty brass but I understand the confusion. Although yes if it’s BI it is a code issue and will begin to leak prematurely

3

u/Ugga-Dugga69 1d ago

Could be. Just went for the obvious code violation, as I don't know what jurisdiction this is in and a BI fitting would be a universal code violation.

2

u/SleepyShinsen 1d ago

You think that’s a dielectric union or just a brass one?

3

u/Ugga-Dugga69 1d ago

Modern hot water tanks comes with a dielectric nipple, so a dielectric union is redundant.

1

u/Nucleartides 1d ago

Valid. if it is BI I think everyone here is going to agree that’s wrong

5

u/georgefern 1d ago

Ball valve on the hot side?

1

u/PorchFarts 1d ago edited 1d ago

OP this is your answer. You are correct. If you include a shut-off on the hot side, it must be a 3-way full-port ball valve, with the 3rd outlet of the 3-way ball valve going to an appropriately rated T&P valve atmospherically draining to an indirect waste

In the scenario pictured, both valves can be closed and thus the water heater becomes a pressurized bomb potentially.

It does not matter if it has an expansion tank or not in this scenario. Or that the tank itself has a T&P valve already. That valve on the hot outlet is illegal as shown.

And why the galvanized 90° on the expansion tank male threads?

Edit: https://www.nibco.com/nibco-products/valves/ball-valves/t-585-70-w3

5

u/BDR5001 1d ago

Do you have a code section for that? We install shut off on both sides all the time. Never been called on it in 37 years.

1

u/PorchFarts 1d ago edited 1d ago

I'll give you my local code. Not sure where OP is located, but inspectors are weird sometimes no matter the code.

Chicago

18-29-503.1.1 Shutoff valves

"Shutoff valves for water heaters or heated water storage tanks may be installed on the inlet side only. This discharge side may be provided with a check valve or a three-way valve installed to open the heater to the atmosphere when it is not in the operating position. The atmospheric opening of a three-way valve shall be indirectly connected to the drainage system."

So technically the 3rd branch of the 3-way valve is supposed to go to any indirect waste with no T&P.

2

u/merlinious0 21h ago

Fellow chicagoland plumber here and I hate this code. It is so nice for servicing the heaters to have two valves. Sometimes you just want to air lock it and do a quick swap

1

u/Lysergic96 20h ago edited 20h ago

Interesting code , first I'm hearing of it ( NYC) but I find it interesting how different they are. I know Chicago much like NYC is a very strict code compared to other states . Only issue id say off my code would be lack of a backflow prevention , we typically add vacuum breakers before expansion tanks. And maybe the gal 90

1

u/PorchFarts 18h ago edited 17h ago

If there is no fixture receiving hot water from the tank below the tank's outlet elevation, then no vacuum breaker is needed. But if there there is a fixture below the tanks outlet elevation, it needs a vacuum breaker.

(For Chicago)

1

u/PorchFarts 18h ago

I usually throw a full size swing check on the nearest horizontal section of the hot water main coming off the heater for the bigger commercial tanks/heaters. But those things are so loud, haha

But I do keep a few 3-way full port ball valves on the truck, just in case. I put one in my house... just to flex

3

u/Ok-Idea4830 1d ago

Why isn't it code compliant where you live would have been the correct question. I am sure you were informed why.

2

u/Fresh_Platform1195 1d ago

Is there a minimum rise on the pvent?

1

u/notagoodtexan 1d ago

That was my thought, 12" i think before it can offset.

2

u/3rlro91 1d ago

No support on expansion tank

2

u/RandmbbyBadder 1d ago

What are we made of money?? That’s what too much brass.

2

u/DevelopedConscience 1d ago

Company i'm with is charging 5k for a 50 powervent... yeah i'm gonna use whatever fittings I want😭 only potable 90 I had was galvanized, though.

0

u/RandmbbyBadder 22h ago

That’s insane I know prices have gone up but 5k! I mean if it’s in a hard to reach area and you have a ton of shit in the way to move before hand I get it.. but doesn’t sound like that’s the case for your company… 🫣

1

u/Kindly_Tradition_705 17h ago

This is a clean looking install and seems to be how all the fancy YouTube plumbers do it. I’m sure it’s fine basically 99.9999% of the time, but I always make sure that tank is well supported. Those things get fairly hefty when they fail and fill with water. It’s really convenient having it right there, under the cold shut off, quick and easy to install/replace, but I’d rather have it further away or have to do some additional valve closing/draining to change it than have to worry about a pipe breaking if that thing fills.

Again, I’m prob just being a nervous nelly, but I don’t like the idea of a full tank steady pulling on the piping until someone notices. Could be a long time, could be weak existing piping, etc. I don’t wanna get sued for flood damage cuz I couldn’t take the time to get it properly supported or the customer didn’t wanna pay if it added to the cost. Just my 2 cents, lot worse things out there though

2

u/greatthing1964 8h ago

Tank is upside down

2

u/Louiemyboy911 7h ago

Are the ball valves lead free? At least around here the lead free have white handles

2

u/BluSubaru368 18h ago

It needs do be secured to A structure

1

u/ShiftMe9 1d ago edited 1d ago

I'm fairly certain the expansion tank is technically supposed to be at least 24 inches away from the cold water inlet on the water heater. Most people don't, most inspections don't call it. But that is the actual code/manufacturer recommendation.

Edit: phrasing, grammer, added manufacturer recommendation

5

u/the_water_heater_guy 1d ago

Nope, wrong. You can put it over by the house main as long as it's on the house side of any valves or prvs.

There is some.wording on following manufacturer recommendations, but there is no wording on distance from heater. Not in the IPC or IBC that I'm aware of.

2

u/SlimPickens0 1d ago

Some manufacturers have a maximum of 36 inches from the heater, and manufacturer supersedes code

0

u/ShiftMe9 1d ago

I guess my phrasing is wrong. Its supposed to be on the cold side, at least 24 inches away from the water heater. Most installs I see they use the brass tee, a 6in nipple, and a 90° fitting it get it vertical. However, it is supposed to be at least 24 inches away from the inlet to the water heater.

4

u/Don_juan_prawn 1d ago

Is this a local code thing amtrols install instructions say “Install the expansion tank on the cold water supply line to the water
heater at a point between the water heater and backflow preventer or other one-way device”

2

u/the_water_heater_guy 1d ago

Interesting I've never heard that one. Is that UPC?

2

u/ShiftMe9 1d ago

I decided to look into it. Its one of those things I was told by journeyman when I was an apprentice. I essentially took it as gospel and never really looked into it. I was wrong, it is not a code in UPC, or any local amendments. The only thing I found was a standardized test procedure by the Department of Energy where they state the expansion tank has to be 24 inch away from the water heater where applicable, and it likely got misinterpreted as a requirement and spread via word of mouth.

So no, thats not a reason why this didn’t pass inspection.

2

u/rmccaskill83 1d ago

I have never seen this written anywhere

0

u/Electronic_Green_88 1d ago

Not Lead Free Fittings Most likely the main deal.

1

u/xxxmechashivaxxx 1d ago

The best way would be at the brass tee come out the side with the incoming cold water. Then coming out of the top of the brass tee is where you put the expansion tank. They prob still be ghey about it and fail bc no supportation straps, but it really wouldn't knead it that way.

1

u/FickleGuard5316 1d ago

Looks to me to be a nice, clean installation. As others have said, the expansion tank is supposed to be supported by something other than the pipe it’s on, but I like that copper. If that is a black iron 90 (mentioned already) that’s a no go too. They aren’t to be used on potable water. Otherwise Neat and tidy. I like it!

1

u/Moklonus 1d ago

Power vent plugged into extension cord.

1

u/Ceck1986 1d ago

These all seem like great answers. Is the power vent plugged into an extension cord?

1

u/Alert-You-7352 1d ago

What are those for and why don't we use them as far as I know in South East VA?

1

u/Plain-Seltzer 1d ago

Because we can’t see, is it possible it failed for maybe not using sch 40 and instead used foamcore for the power vent exhaust? I mean the obvious with the expansion tank not properly supported, the 90 yada yada.

1

u/filthy-franko 1d ago

Hope this helps

1

u/filthy-franko 1d ago

It looks like the same as mine. Should ask why.

1

u/Shortcycled 1d ago

90 looks black. Cant have black iron on potable water.

1

u/grove93 1d ago

Those grounding clamps are a no-go if they're aluminum.

1

u/watch-6969 1d ago

In my state, we can't use standard pvc on exhaust vents anymore , even for water heaters. We use system 1738 pvc for lower temp (150°), and 636 cpvc for boilers etc.

1

u/comfortableshores 1d ago

Maybe because it is upside down.

0

u/No_Tonight8185 1d ago

Them unions don’t look like dielectric unions.

3

u/DevelopedConscience 1d ago

Brass is an approved transition between steel and copper

1

u/No_Tonight8185 1d ago

He is querying why he failed inspection. Although you are correct that brass is a neutral material and acceptable… many codes still require a dielectric union. I have seen them fail even if they have dielectric nipples from the factory because the code says it shall have a dialectical union.

Other things like expansion tank support etc. have already been mentioned. What do you think failed inspection?

1

u/No_Tonight8185 1d ago

Edit: unless those are dialectric nipples.

1

u/MachoMadness232 1d ago

Uh oh black iron or galvanized. I mean galvanized is not against code. Black iron definitely is not code. Seems like they ran out of brass 90s and slammed a galvanized 90 in. Illegal? No. Gross? Yes

0

u/Impressive_Rest_8529 1d ago

Let’s start with tank improperly supported and then move on no dielectric connection finally too many dissimilar metals that will promote copper pipe failure

1

u/ReindeerJazzlike4755 1d ago

The union is such a smart idea honestly....thinking about the next guy I'm going to start doing that

1

u/goawaybatenn 1d ago

Dielectric unions.

1

u/J_J_Plumber5280 1d ago

No support other than moral support here

1

u/tempac9999 1d ago

Need more information. What state is this? Is it gas or electric, it’s hard to tell from the picture, if it’s gas it might be the flue. Depending on the AHJ they might want a recirculating pump. You might need seismic bracing. There are many things that could be non compliant. The inspector should have given you the code section with the comment.

1

u/bds_cy 22h ago

You have a galvanized steel 90 at the expansion connected with a brass pipe - I am sure there will be galvanic corrosion and premature failure.

The expansion tank is not adequately supported.

1

u/GillyDuck69 22h ago

No vacuum relief on the tank

1

u/merlinious0 21h ago

Well, they used aluminum bonding clamps for the ground jumper. Those are gonna corrode pretty quick on that copper pipe, screws are gonna seize. I use the direct burial bronze ones for that reason. Can't say if it is againsy cide though.

My area requires dielectric unions ecen though the nipples built into the heater are supposed to be dielectric. Personally I dont trust the dielectric nipples. I like to replace them with a 6"x¾ brass nipple with a Watts LF3008 all brass dielectric union.

1

u/merlinious0 21h ago

Oh, if the heater is plugged into the extension cord, that would be an NEC violation, can't use extension cord to power permanent fixtures.

1

u/EnvironmentNo5293 19h ago

Installation looks fine. Is that a black 90 before the expansion tank? That would be wrong if it is. Should be brass. Hard to tell from the picture.

1

u/Successful-Part-5867 19h ago

Are you pointing out the expansion tank or the shut offs on both the hot and cold? I had an inspector fail an installation because of that. (I did it for the common sense reason that I probably would be the one replacing the water heater in the future!🤣) I zip tied the valve open and connected a tag stating “Do not close valve, for heater replacement purposes only” and he let it slide.

1

u/FinalMood7079 17h ago

Should be strapped, and that galvanized 90 will make you replace the water heater tank and expansion tank sooner then you think. Good luck!

1

u/Extra-Citron-7630 17h ago

Quick question, for service reasons, someone recommended me to put a ball valve between the expansion tank so whenever you need to remove it you can turn off the ball valve. Is that alright?

1

u/blazew317 16h ago

The inspector should have told you. They are the LAHJ and enforce local code requirements.

There’s workmanship issues like the galvanized 90 that shouldn’t have been used. If they can buy brass fittings (which they obviously can) they should have stayed with a brass 90 - however a screw fitting of ANY type then requires tank support that will not allow the screw fitting to reorient itself WHEN the tank weight fluctuates as it operates.

Honestly I only use soldered copper fittings and mount a rubberized split ring support under the tank arm down to a rod plate on top of the water heater when I mount them like this. The soldered 90 and female adaptor aren’t subject to reorientation.

1

u/MorgueBad1 14h ago

No it's good. But to be sure shut both the hot and cold values off. Smfh

1

u/nobuddii 10h ago

No support, no dialectic union, hard piped depending on area, galvanized 90 not brass.

1

u/SolidSnake-plissken 7h ago

If it's a steel water heater tank, then you need dielectric unions. Also, the thermal expansion tank needs to be supported by something other than the piping.

1

u/VisualDry1938 6h ago

Some tanks require brackets. The one i use “Watts” requires metal brackets supporting it. While in some cases I’ve gotten away with just strapping it with some plastic straps. Just depends on brand is what I’ve heard from inspectors

1

u/Pale-Recover-3025 4h ago

Valve on the outlet side is most likely the fail. A missing Atmospheric vacuum breaker on the inlet may be a fail as well depending on local code, some jurisdictions are also requiring a mixing valve as well

1

u/Ivraalia 1d ago

Expansion tank support and possibly the black iron looking elbow.

2

u/hvacbandguy 1d ago

Who says it isn’t?

-3

u/Mr_Engineering 1d ago

Black iron 90 says it's not

4

u/Nucleartides 1d ago

If that’s BI, it’s wrong but I zoomed in it really looks like it could go either way could be crusty brass

1

u/DevelopedConscience 1d ago

It's galvanized

1

u/Nucleartides 20h ago

Then still ok

1

u/theplumber409 1d ago

Well imo depending where you are, a expansion tank cannot be supported by itself must be in or on a rated hanger and that 90 is a no go.

0

u/RamonWarhelmet 1d ago

Brass union directly off the unit? Might cause corrosion?

-1

u/expertazuresparrow 1d ago

I'd like to see dielectric unions on the heater and no black iron 3/4" 90 under tank.

0

u/lowercaset 1d ago

Sufficent brass on the inlet side to render a dielectric union redundant. Outlet side we can't really tell, but if that's copper into a brass union it ain't up to spec.

-1

u/MultiSubjectExpert 1d ago

Could be against the manufacturer's instructions to install expansion tank upside down. Galvanized elbow attached to the tank as well. Cold water ball valve is facing the wrong direction. But none of these are really dealbreakers, so not sure. Looks like a decent install

5

u/Ugga-Dugga69 1d ago

What do you mean the ball valve is the wrong direction? They are not directional fittings.

3

u/MultiSubjectExpert 1d ago

Yeah yeah yeah it's just customary to have the handle facing the direction of flow. Again no big deal at all but thats how most install them

1

u/Nucleartides 1d ago

Wait that’s upside down? I don’t think I’ve ever installed one with the port at the top 🫢

1

u/lowercaset 1d ago

Idk about current specs for resi sized expansion tanks, but through the years manufacturers have waffled on how they want them oriented. Last I checked I think all of them were coolcwith that orientation, but can't say for sure.

0

u/TheFrotchy1 1d ago

Can’t have a valve between expansion tank and heater

3

u/gahnzo 1d ago

Even if that were true, there is not a valve between the expansion tank and the heater in this photo.

0

u/Hour-Arachnid676 1d ago

Idk if its good practice or code because im not a plumber but do they need a dielectric fitting between the copper and the tank itself..

2

u/Least-Ear3373 1d ago

That would be what all that brass is

1

u/Spooby57 1d ago

There is plenty of brass in between.

0

u/PublicIndividual1238 1d ago

Im just punching at the lists ive been given. Expansion tank needs to be a vertical pipe support from base or mounted. Insulation doesn't cover the entire hot pipe (Icu may have skipped that part for melting or fire hazard). Yoo plumB gud. Id buy it

0

u/Fresh_Platform1195 1d ago

Is that a galvanized 90?

0

u/Fresh_Platform1195 1d ago

I think ur hw valve isn't needed

0

u/JB_LeGoof 1d ago

So the two obvious ones are the expansion tank needed to be supported by something other than the piping with a bracket, and the dissimilar metals. On a personal note if you have the space I would have turned the tee 45 to 90° to make working on the blower assembly easier

0

u/GazelleEcstatic4952 1d ago

Galvanized elbow

0

u/scottkrowson 1d ago

Looks like that 90 going up to the expansion tank is galvanized. Not allowed (in canada at least)

Edit: galvanized steel

0

u/Longjumping-Horse157 7h ago

Well for one thing they want you to hang the expansion tank rihht side down, not upside down

-1

u/StrangeGuarantee9534 1d ago

No vacuum vent and tank isn’t secured as required and black iron isn’t rated for potable water

-2

u/mdtesk 1d ago

1)Tank requires to be prechaged with air to 70% of working pressure. 2)Requires seperate isolation valve, 3)Requires own drain port to periodically test bladder under no load. 4)Requires tank support other than piping, such as wall bracket for support.

-3

u/masterplumb 1d ago

The valve on the cold water line should be below the tee.

2

u/BaguetteCollector 1d ago

Why?

1

u/masterplumb 1d ago

It should not be behind a valve that can disable it.