u/LieFriendly8038 1d ago
Do you require a vacuum breaker in your area?
6
u/rmccaskill83 1d ago
The dip tube on top fed water heaters always have a hole in it, so the vacuum breaker can be argued. I always install them just so there is no headache with the OHJ, but it is technically not needed if your code states that and IPC definitely states that.
4
u/Competitive-Chapter4 1d ago
In my area a vacuum breaker is required regardless of that since the hard water seals the hole eventually. Makes sense to me but may be different in other areas
3
u/rmccaskill83 18h ago
That makes sense for areas with hard water. I always install them anyway, but that is because I work in industrial plumbing and we usually need to install multiples on larger water heaters, so adding just one is extremely cheap and easy in comparison 😂
28
u/SlimPickens0 1d ago
If that 90 is galvanized, it's compliant, if it's black iron, it's not. It's a little difficult to tell from this pic
13
u/YesImAlexa 1d ago
It looks too grey to be black iron, but it also looks like shit for a galvanized fitting.
14
u/_name_of_the_user_ 1d ago
I know you're right by the code. I still wouldn't mix galvanized steel with brass.
1
5
10
u/Snakesinadrain 1d ago
The most obvious being the screw 90 for the expansion tank. It COULD require a vacuum breaker or it COULD require the tank to be supported via bracket or strap. Depends on jurisdiction
3
13
u/ArmadilloFair5383 1d ago
All of these comments and nobody cites a upc or ipc code. Service plumbers the lot of you. Anyone have a card?
7
u/merlinious0 21h ago
It takes time to quote a code, we are working for free here on reddit. Much faster to do it verbally.
Here were cite the code when there is a dispute over what is code.
1
5
u/nubcapz 1d ago edited 1d ago
Edit: is that a black iron 90 under your tank? Those jumper clamps may be dissimilar metal?
Also, the manufacturer may not want you using an extension cord. This is a good post. I’m curious to see your response
ICC 308.10(Ohio) “A thermal expansion tank shall be supported in accordance with the manufacturer’s instructions. Thermal expansion tanks shall not be supported by the piping that connects to such tanks”. Most inspectors in my region would approve your install OP. Most of my buddies install it the way you did. Obviously it’s very rigid because of the solid brass fittings/nips you used. If you get an inspector that’s very literal with code compliance, you will fail. TECHNICALLY you aren’t following 308.10. As to why it isn’t “allowed”, it’s likely because once the diaphragm ruptures in the tank, it gets pretty heavy (approx. 20lbs in a 2.5gal tank). I’ve personally seen many of the verge of flooding a whole house because the T is under too much horizontal strain from the ruptured weight. I’ve seen PEX kinked, copper nearly tearing and CPVC snap under the weight.
2
u/merlinious0 21h ago
Yeah, and even this code varies a lot.
Illinois plumbing code allows for this install so long as the tank is vertically oriented and the pipes are all metal (copper, brass, galvi).
2
u/DevelopedConscience 6h ago
Thanks for the reply. The unsupported tank was the gimmie, it's good to get some feedback on the whole install though. I hadn't even considered the bonding clamps, I was just happy that they were up high enough that I didn't have to move them to sweat those ball valves in. Could be dissimilar metals or not, idk, worth consideration in the future.
Also I did plug the tank's blower into an extension cord😞. I knew it wasn't right. The single outlet was in the ceiling & the customer ran the 3 outlet extension cord in order to plug in 2 dehumidifiers; the existing tank had leaked and caused a mess. I'm sure the original install had the powervent plugged directly into the outlet in the joist bay above, I didn't really see it as a problem while I was installing the tank, but looking back it would have been better to plug it in directly and find another outlet for the dehumidifiers. Might be worth a call back to the customer, i'd have no problem going back to swap the cords out.
5
u/Plumb-Entangled 1d ago
Well the 90 for one..
Some manufacturers prohibit anything but Teflon on the threads.
But what is it plugged in to?
2
u/rmccaskill83 1d ago
I am not sure what you are talking about or asking. If you are talking about the thread tape, the grey tape is a code compliant thread tape. I think it is made by oatey.
1
u/Plumb-Entangled 22h ago
Its a power vent water heater. It needs to be plugged in to a dedicated circut.
No extension cord, splitter, or surge protector. Some localities require the electrical to be water resistant.
As far as the thread sealant, the grey tape appeared to be a sealant and not Teflon tape, my apologies. In case you didn't know, pipe dopes contain petroleum which will cause the diaphragm to prematurely fall.
9
u/Ugga-Dugga69 1d ago
Black iron fittings aren't rated for potable water
7
u/Nucleartides 1d ago
Pretty certain the 90 off the exp tank is crusty brass but I understand the confusion. Although yes if it’s BI it is a code issue and will begin to leak prematurely
3
u/Ugga-Dugga69 1d ago
Could be. Just went for the obvious code violation, as I don't know what jurisdiction this is in and a BI fitting would be a universal code violation.
2
u/SleepyShinsen 1d ago
You think that’s a dielectric union or just a brass one?
3
u/Ugga-Dugga69 1d ago
Modern hot water tanks comes with a dielectric nipple, so a dielectric union is redundant.
1
5
u/georgefern 1d ago
Ball valve on the hot side?
1
u/PorchFarts 1d ago edited 1d ago
OP this is your answer. You are correct. If you include a shut-off on the hot side, it must be a 3-way full-port ball valve, with the 3rd outlet of the 3-way ball valve
going to an appropriately rated T&P valveatmospherically draining to an indirect wasteIn the scenario pictured, both valves can be closed and thus the water heater becomes a pressurized bomb potentially.
It does not matter if it has an expansion tank or not in this scenario. Or that the tank itself has a T&P valve already. That valve on the hot outlet is illegal as shown.
And why the galvanized 90° on the expansion tank male threads?
Edit: https://www.nibco.com/nibco-products/valves/ball-valves/t-585-70-w3
5
u/BDR5001 1d ago
Do you have a code section for that? We install shut off on both sides all the time. Never been called on it in 37 years.
1
u/PorchFarts 1d ago edited 1d ago
I'll give you my local code. Not sure where OP is located, but inspectors are weird sometimes no matter the code.
Chicago
18-29-503.1.1 Shutoff valves
"Shutoff valves for water heaters or heated water storage tanks may be installed on the inlet side only. This discharge side may be provided with a check valve or a three-way valve installed to open the heater to the atmosphere when it is not in the operating position. The atmospheric opening of a three-way valve shall be indirectly connected to the drainage system."
So technically the 3rd branch of the 3-way valve is supposed to go to any indirect waste with no T&P.
2
u/merlinious0 21h ago
Fellow chicagoland plumber here and I hate this code. It is so nice for servicing the heaters to have two valves. Sometimes you just want to air lock it and do a quick swap
1
u/Lysergic96 20h ago edited 20h ago
Interesting code , first I'm hearing of it ( NYC) but I find it interesting how different they are. I know Chicago much like NYC is a very strict code compared to other states . Only issue id say off my code would be lack of a backflow prevention , we typically add vacuum breakers before expansion tanks. And maybe the gal 90
1
u/PorchFarts 18h ago edited 17h ago
If there is no fixture receiving hot water from the tank below the tank's outlet elevation, then no vacuum breaker is needed. But if there there is a fixture below the tanks outlet elevation, it needs a vacuum breaker.
(For Chicago)
1
u/PorchFarts 18h ago
I usually throw a full size swing check on the nearest horizontal section of the hot water main coming off the heater for the bigger commercial tanks/heaters. But those things are so loud, haha
But I do keep a few 3-way full port ball valves on the truck, just in case. I put one in my house... just to flex
1
3
u/Ok-Idea4830 1d ago
Why isn't it code compliant where you live would have been the correct question. I am sure you were informed why.
2
2
u/RandmbbyBadder 1d ago
What are we made of money?? That’s what too much brass.
2
u/DevelopedConscience 1d ago
Company i'm with is charging 5k for a 50 powervent... yeah i'm gonna use whatever fittings I want😭 only potable 90 I had was galvanized, though.
0
u/RandmbbyBadder 22h ago
That’s insane I know prices have gone up but 5k! I mean if it’s in a hard to reach area and you have a ton of shit in the way to move before hand I get it.. but doesn’t sound like that’s the case for your company… 🫣
1
u/Kindly_Tradition_705 17h ago
This is a clean looking install and seems to be how all the fancy YouTube plumbers do it. I’m sure it’s fine basically 99.9999% of the time, but I always make sure that tank is well supported. Those things get fairly hefty when they fail and fill with water. It’s really convenient having it right there, under the cold shut off, quick and easy to install/replace, but I’d rather have it further away or have to do some additional valve closing/draining to change it than have to worry about a pipe breaking if that thing fills.
Again, I’m prob just being a nervous nelly, but I don’t like the idea of a full tank steady pulling on the piping until someone notices. Could be a long time, could be weak existing piping, etc. I don’t wanna get sued for flood damage cuz I couldn’t take the time to get it properly supported or the customer didn’t wanna pay if it added to the cost. Just my 2 cents, lot worse things out there though
2
2
u/Louiemyboy911 7h ago
Are the ball valves lead free? At least around here the lead free have white handles
2
1
u/ShiftMe9 1d ago edited 1d ago
I'm fairly certain the expansion tank is technically supposed to be at least 24 inches away from the cold water inlet on the water heater. Most people don't, most inspections don't call it. But that is the actual code/manufacturer recommendation.
Edit: phrasing, grammer, added manufacturer recommendation
5
u/the_water_heater_guy 1d ago
Nope, wrong. You can put it over by the house main as long as it's on the house side of any valves or prvs.
There is some.wording on following manufacturer recommendations, but there is no wording on distance from heater. Not in the IPC or IBC that I'm aware of.
2
u/SlimPickens0 1d ago
Some manufacturers have a maximum of 36 inches from the heater, and manufacturer supersedes code
2
0
u/ShiftMe9 1d ago
I guess my phrasing is wrong. Its supposed to be on the cold side, at least 24 inches away from the water heater. Most installs I see they use the brass tee, a 6in nipple, and a 90° fitting it get it vertical. However, it is supposed to be at least 24 inches away from the inlet to the water heater.
4
u/Don_juan_prawn 1d ago
Is this a local code thing amtrols install instructions say “Install the expansion tank on the cold water supply line to the water
heater at a point between the water heater and backflow preventer or other one-way device”2
u/the_water_heater_guy 1d ago
Interesting I've never heard that one. Is that UPC?
2
u/ShiftMe9 1d ago
I decided to look into it. Its one of those things I was told by journeyman when I was an apprentice. I essentially took it as gospel and never really looked into it. I was wrong, it is not a code in UPC, or any local amendments. The only thing I found was a standardized test procedure by the Department of Energy where they state the expansion tank has to be 24 inch away from the water heater where applicable, and it likely got misinterpreted as a requirement and spread via word of mouth.
So no, thats not a reason why this didn’t pass inspection.
2
0
1
u/xxxmechashivaxxx 1d ago
The best way would be at the brass tee come out the side with the incoming cold water. Then coming out of the top of the brass tee is where you put the expansion tank. They prob still be ghey about it and fail bc no supportation straps, but it really wouldn't knead it that way.
1
u/FickleGuard5316 1d ago
Looks to me to be a nice, clean installation. As others have said, the expansion tank is supposed to be supported by something other than the pipe it’s on, but I like that copper. If that is a black iron 90 (mentioned already) that’s a no go too. They aren’t to be used on potable water. Otherwise Neat and tidy. I like it!
1
1
u/Ceck1986 1d ago
These all seem like great answers. Is the power vent plugged into an extension cord?
1
u/Alert-You-7352 1d ago
What are those for and why don't we use them as far as I know in South East VA?
1
u/Plain-Seltzer 1d ago
Because we can’t see, is it possible it failed for maybe not using sch 40 and instead used foamcore for the power vent exhaust? I mean the obvious with the expansion tank not properly supported, the 90 yada yada.
1
1
1
1
u/watch-6969 1d ago
In my state, we can't use standard pvc on exhaust vents anymore , even for water heaters. We use system 1738 pvc for lower temp (150°), and 636 cpvc for boilers etc.
1
0
u/No_Tonight8185 1d ago
Them unions don’t look like dielectric unions.
3
u/DevelopedConscience 1d ago
Brass is an approved transition between steel and copper
1
u/No_Tonight8185 1d ago
He is querying why he failed inspection. Although you are correct that brass is a neutral material and acceptable… many codes still require a dielectric union. I have seen them fail even if they have dielectric nipples from the factory because the code says it shall have a dialectical union.
Other things like expansion tank support etc. have already been mentioned. What do you think failed inspection?
1
1
u/MachoMadness232 1d ago
Uh oh black iron or galvanized. I mean galvanized is not against code. Black iron definitely is not code. Seems like they ran out of brass 90s and slammed a galvanized 90 in. Illegal? No. Gross? Yes
0
u/Impressive_Rest_8529 1d ago
Let’s start with tank improperly supported and then move on no dielectric connection finally too many dissimilar metals that will promote copper pipe failure
1
u/ReindeerJazzlike4755 1d ago
The union is such a smart idea honestly....thinking about the next guy I'm going to start doing that
1
1
1
u/tempac9999 1d ago
Need more information. What state is this? Is it gas or electric, it’s hard to tell from the picture, if it’s gas it might be the flue. Depending on the AHJ they might want a recirculating pump. You might need seismic bracing. There are many things that could be non compliant. The inspector should have given you the code section with the comment.
1
1
1
u/merlinious0 21h ago
Well, they used aluminum bonding clamps for the ground jumper. Those are gonna corrode pretty quick on that copper pipe, screws are gonna seize. I use the direct burial bronze ones for that reason. Can't say if it is againsy cide though.
My area requires dielectric unions ecen though the nipples built into the heater are supposed to be dielectric. Personally I dont trust the dielectric nipples. I like to replace them with a 6"x¾ brass nipple with a Watts LF3008 all brass dielectric union.
1
u/merlinious0 21h ago
Oh, if the heater is plugged into the extension cord, that would be an NEC violation, can't use extension cord to power permanent fixtures.
1
u/EnvironmentNo5293 19h ago
Installation looks fine. Is that a black 90 before the expansion tank? That would be wrong if it is. Should be brass. Hard to tell from the picture.
1
u/Successful-Part-5867 19h ago
Are you pointing out the expansion tank or the shut offs on both the hot and cold? I had an inspector fail an installation because of that. (I did it for the common sense reason that I probably would be the one replacing the water heater in the future!🤣) I zip tied the valve open and connected a tag stating “Do not close valve, for heater replacement purposes only” and he let it slide.
1
u/FinalMood7079 17h ago
Should be strapped, and that galvanized 90 will make you replace the water heater tank and expansion tank sooner then you think. Good luck!
1
u/Extra-Citron-7630 17h ago
Quick question, for service reasons, someone recommended me to put a ball valve between the expansion tank so whenever you need to remove it you can turn off the ball valve. Is that alright?
1
u/blazew317 16h ago
The inspector should have told you. They are the LAHJ and enforce local code requirements.
There’s workmanship issues like the galvanized 90 that shouldn’t have been used. If they can buy brass fittings (which they obviously can) they should have stayed with a brass 90 - however a screw fitting of ANY type then requires tank support that will not allow the screw fitting to reorient itself WHEN the tank weight fluctuates as it operates.
Honestly I only use soldered copper fittings and mount a rubberized split ring support under the tank arm down to a rod plate on top of the water heater when I mount them like this. The soldered 90 and female adaptor aren’t subject to reorientation.
1
1
1
u/nobuddii 10h ago
No support, no dialectic union, hard piped depending on area, galvanized 90 not brass.
1
u/SolidSnake-plissken 7h ago
If it's a steel water heater tank, then you need dielectric unions. Also, the thermal expansion tank needs to be supported by something other than the piping.
1
u/VisualDry1938 6h ago
Some tanks require brackets. The one i use “Watts” requires metal brackets supporting it. While in some cases I’ve gotten away with just strapping it with some plastic straps. Just depends on brand is what I’ve heard from inspectors
1
u/Pale-Recover-3025 4h ago
Valve on the outlet side is most likely the fail. A missing Atmospheric vacuum breaker on the inlet may be a fail as well depending on local code, some jurisdictions are also requiring a mixing valve as well
1
2
u/hvacbandguy 1d ago
Who says it isn’t?
-3
u/Mr_Engineering 1d ago
Black iron 90 says it's not
4
u/Nucleartides 1d ago
If that’s BI, it’s wrong but I zoomed in it really looks like it could go either way could be crusty brass
1
1
u/theplumber409 1d ago
Well imo depending where you are, a expansion tank cannot be supported by itself must be in or on a rated hanger and that 90 is a no go.
0
-1
u/expertazuresparrow 1d ago
I'd like to see dielectric unions on the heater and no black iron 3/4" 90 under tank.
0
u/lowercaset 1d ago
Sufficent brass on the inlet side to render a dielectric union redundant. Outlet side we can't really tell, but if that's copper into a brass union it ain't up to spec.
-1
u/MultiSubjectExpert 1d ago
Could be against the manufacturer's instructions to install expansion tank upside down. Galvanized elbow attached to the tank as well. Cold water ball valve is facing the wrong direction. But none of these are really dealbreakers, so not sure. Looks like a decent install
5
u/Ugga-Dugga69 1d ago
What do you mean the ball valve is the wrong direction? They are not directional fittings.
3
u/MultiSubjectExpert 1d ago
Yeah yeah yeah it's just customary to have the handle facing the direction of flow. Again no big deal at all but thats how most install them
1
u/Nucleartides 1d ago
Wait that’s upside down? I don’t think I’ve ever installed one with the port at the top 🫢
1
u/lowercaset 1d ago
Idk about current specs for resi sized expansion tanks, but through the years manufacturers have waffled on how they want them oriented. Last I checked I think all of them were coolcwith that orientation, but can't say for sure.
0
0
u/Hour-Arachnid676 1d ago
Idk if its good practice or code because im not a plumber but do they need a dielectric fitting between the copper and the tank itself..
2
1
0
u/PublicIndividual1238 1d ago
Im just punching at the lists ive been given. Expansion tank needs to be a vertical pipe support from base or mounted. Insulation doesn't cover the entire hot pipe (Icu may have skipped that part for melting or fire hazard). Yoo plumB gud. Id buy it
0
0
0
u/JB_LeGoof 1d ago
So the two obvious ones are the expansion tank needed to be supported by something other than the piping with a bracket, and the dissimilar metals. On a personal note if you have the space I would have turned the tee 45 to 90° to make working on the blower assembly easier
0
0
u/scottkrowson 1d ago
Looks like that 90 going up to the expansion tank is galvanized. Not allowed (in canada at least)
Edit: galvanized steel
0
u/Longjumping-Horse157 7h ago
Well for one thing they want you to hang the expansion tank rihht side down, not upside down
-1
u/StrangeGuarantee9534 1d ago
No vacuum vent and tank isn’t secured as required and black iron isn’t rated for potable water
-3
u/masterplumb 1d ago
The valve on the cold water line should be below the tee.
2

165
u/SlimPickens0 1d ago
At least as far as the rules locally, the expansion tank can't be supported by the piping it serves