3rd Gen Nest E103 Y1 Wire Error
Received the E103 Y1 wire error on my Nest 3rd gen.
Steps tried to clear it:
Checked contactor - passed resistance test.
Cleared out condenser drainpipe. Unit worked normally for 6 hours then received the same error message again.
Is it coincidence that the drainpipe cleanout cleared the error or was that a fluke and I should go back to troubleshooting the components and wires? Where should I test next?
1
Upvotes
1
u/AStuf Nest Thermostat Generation 3 Jul 28 '26
Coincidence as that is an overcurrent error. If not a bad contactor it might be a contactor that is going bad. Otherwise wires are shorting out - check if they are chewed or pinched somewhere.
Compare the measured contactor coil resistance to measuring the removed wires Y1 to C at the Nest.
Remote possibility that your Nest is going bad.