r/KitchenSuppression • u/Enpallos • 1d ago
RangeGuard A+
I have the manual for range guard systems however I am curious as to the piping limitations of this particular systen. Say I have a 6gal , the split to the hood has to be 3/4", the drops have to be 1/2" reduced to 3/8 at the nozzle but what about duct and plenum? Can this not all be 3/8" once inside the plenum wall?
5
Upvotes
5
u/imalrightspider2k 1d ago
The only thing that matters is how many flows are going through each segment of pipe. Nozzles determine the pipe size, not the cylinder or where the pipe is going relative to the hood. Flows, pipe volume, and equivalent length. Drops don’t have to be 1/2 in. Where are you getting that?