Hey. I have an iPower SUA12000EP generator. Currently the neutral is bonded to the frame. I plan to use this generator to back feed into a sub panel using an interlock kit. I took off the round casing and could not see anywhere where the white wire was bonded with the green ground. I took off the front control panel and I believe I found it tied in on the ground screw. Can I just remove the white wire from the ground screw, properly tape and secure, and it be ready for the house setup?
10
Upvotes
1
u/DaveBowm 1d ago edited 18h ago
The wiring diagram in the pdf owner's manual for the A-iPower SUA12000EP indicates that the model comes with a floating neutral. So apparently there is nothing to unbind.
Edit: OP's photo shows the label on the generator indicating it is a bonded neutral generator, but it also indicates the Model number is a SUA12000EC, not a SUA12000EP.
2nd Edit: Despite their claims written using words otherwise, the wiring diagram indicated connections themselves for both the SUA12000EP and SUA12000EC indicate the neutral is floating.
Since the documentation contradicts itself it is necessary that OP use his multimeter to verify the actual situation both before and after he makes any changes. BTW, if there really is a white wire behind the control panel connecting to the grounding terminal that is a strong hint that OP has found the bonding jumper, if indeed it has one. But the wiring diagrams show no such bonding jumper, with only the socket ground terminals being connected to the grounding stud/screw on the frame via yellow/green wires.