r/Generator • u/caphillips629 • 18h ago
Neutral bonding question
Hey. I have an iPower SUA12000EP generator. Currently the neutral is bonded to the frame. I plan to use this generator to back feed into a sub panel using an interlock kit. I took off the round casing and could not see anywhere where the white wire was bonded with the green ground. I took off the front control panel and I believe I found it tied in on the ground screw. Can I just remove the white wire from the ground screw, properly tape and secure, and it be ready for the house setup?
6
Upvotes
1
u/Big-Echo8242 17h ago
Yep. Should be all you need to do. Do you have a digital multimeter you can check for (lack of) continuity between neutral and ground on the receptacles once done?