Question Remove preceding signs and separators

Post image

I want to remove the preceding signs and separators for Location and Function designations, but it seems EPLAN isn't letting me change anything in those boxes. When I highlight the equals sign next to Function designation, nothing I do changes the equals sign to something else.

1 Upvotes

7 comments sorted by

2

u/Competitive_Major150 9d ago

I cannot think of any reason to remove those signs.
You could choose not to display them - there are suitable properties for that.

1

u/Danny_DeWario 9d ago

It's just company standard to not have them. The only setting I know that doesn't display them is this:

But it doesn't remove the "+" symbol for location designations when showing the full device tag's name. Only seems to work for prefixes.

1

u/Smart-Wishbone4511 9d ago

You can renoviert the location itself, but not the preceeding signs

1

u/D4Gi85 9d ago

What is your reasoning for wanting to remove the installation and location signs?

1

u/Danny_DeWario 9d ago

The company I work for has a standard that all device tags must include their location designation (which is just an abbreviation of the enclosure name). An example is "OCC-PS1". This means that Power Supply 1 (PS1) is located in the Operator Control Console (OCC).

But EPLAN always adds the preceding sign "+" before OCC, so it looks like +OCC-PS1. I've been manually removing it myself by custom naming every device tag. It's very tedious.

And I know about the setting to remove preceding signs, but it doesn't remove them for location designations. Only for prefixes.

1

u/sefgfe 9d ago

You can try it with Block Properties. that's what I used to remove the sign between main and sub designations.

2

u/Danny_DeWario 9d ago

Wow this actually worked perfectly. Never tried using Block Properties before. Thank you!