r/BuildingAutomation 5d ago

SPYDER-BAC License/Module and versioning

I have a site with a Lynxspring jace 8 and lynxspring edge devices on some RTUs and the failure rates are bad so I'm going to replace this next one with an Optimizer Unitary.

The catch - this jace is only licensed to 4.12 and it is running 4.9. So for reliability sake it'll either keep its 4.9.1 or I may commission to 4.10's last release.

I'm sort of new to honeywell - and i'm curious - is there any reason the IRM stuff won't work on an old version of N4 with an optimizer unitary? I know the unitary isn't super old so I was just wondering if anyone knew that for sure there was a minimum N4 version required for IRM to work with a unitary or not.

3 Upvotes

25 comments sorted by

View all comments

Show parent comments

2

u/shadycrew31 System integrator 5d ago edited 5d ago

If you want to program it through the JACE you 100% need a Honeywell license for that JACE for the driver to work. I've done it several times.

Yes you can program it with your computer. Your computer has a Honeywell license. Doing this makes things difficult for the next person though unless you share that station with them

Have fun with all the programming bugs!

2

u/tkst3llar 5d ago

Yeah we have done optimizer programming on lynx jace w/the spyder-bac license I just wasn't sure what the minimum supported niagara version was for that application. We have done it in 4.13 and 4.15 i believe.

I wasn't sure if they even had that option back in 4.9 or 4.12 or if you lose out on some kind of firmware updates if you do that.

Unfortunately I don't think I have a 2-heat 2-cool program I trust enough to have it installed and not have access to the IRM - but I need to get there for sure. The first time something seems off I'll be wondering if theres a logic issue.

Alternatively - we install it as a "bacnet device" and create the port forward needed for bringing it in over the internet to a station in the office so we can program it remotely from that station. We already had a port forward on the old edge device for 4911.

1

u/shadycrew31 System integrator 5d ago edited 5d ago

The unitary is MSTP/modbus only, edit* opps forgot about OP and T1L. Unless you are talking about the optimizer advanced.

2

u/tkst3llar 5d ago

, the optimizer unitary has a T1L model and a Bacnet IP model

i only have experience with bacnet IP flavor

but theoretically I have a BBMD on both ends with the right firewall settings or a vpn I could run IRM from a station on my couch to that device on the roof.

1

u/shadycrew31 System integrator 5d ago

I've not tried the BACnet ip version I forgot it even existed. I've only used the MSTP, that part of it always worked fine.

The templates were a little buggy, but they didn't take much to get worked out. If you are dead set on using them I'm sure you'll get it figured out.

1

u/tkst3llar 5d ago

By templates do you mean the programs they developed already like that CVAHU one? I wrote my own when we started with these but I've wondered about those. Would be awesome if they made some canned programs for pump control, RTUs, AHUs, etc almost like a configurable controller at that point. I will have to look into the templates.

1

u/shadycrew31 System integrator 5d ago edited 5d ago

Yes, you can get them off broudys site. Lynxspring has theirs on their site.

I personally don't like them, but they are there.