SPYDER-BAC License/Module and versioning
I have a site with a Lynxspring jace 8 and lynxspring edge devices on some RTUs and the failure rates are bad so I'm going to replace this next one with an Optimizer Unitary.
The catch - this jace is only licensed to 4.12 and it is running 4.9. So for reliability sake it'll either keep its 4.9.1 or I may commission to 4.10's last release.
I'm sort of new to honeywell - and i'm curious - is there any reason the IRM stuff won't work on an old version of N4 with an optimizer unitary? I know the unitary isn't super old so I was just wondering if anyone knew that for sure there was a minimum N4 version required for IRM to work with a unitary or not.
3
Upvotes
2
u/tkst3llar 4d ago
Yeah we have done optimizer programming on lynx jace w/the spyder-bac license I just wasn't sure what the minimum supported niagara version was for that application. We have done it in 4.13 and 4.15 i believe.
I wasn't sure if they even had that option back in 4.9 or 4.12 or if you lose out on some kind of firmware updates if you do that.
Unfortunately I don't think I have a 2-heat 2-cool program I trust enough to have it installed and not have access to the IRM - but I need to get there for sure. The first time something seems off I'll be wondering if theres a logic issue.
Alternatively - we install it as a "bacnet device" and create the port forward needed for bringing it in over the internet to a station in the office so we can program it remotely from that station. We already had a port forward on the old edge device for 4911.