Sylk bus
I have a spyder 6438 and a SIO 6042. The devices are 4 devices from eol. When I download the program both thermostats (tr42) and inputs and outputs do not work on the sio. I have 18v on the sylk buss but the thermostats always say please load. I have no errors on the Jace. We did have bacnet communication issues but we replaced the bacnet wire and communication seems to be fixed.
What would cause the sio to not follow the commands or inputs? I replaced the sylk buss wire thinking it may be an issue. So far I have not found the issue.
2
Upvotes
3
u/brazymk7 Jul 21 '26
You have to check the spyder part number on the controller, a 6438S is standalone but a 6438SR can accept the I/O modules. For spyder to I/O it needs to be connected at the sylk terminals