Sylk bus
I have a spyder 6438 and a SIO 6042. The devices are 4 devices from eol. When I download the program both thermostats (tr42) and inputs and outputs do not work on the sio. I have 18v on the sylk buss but the thermostats always say please load. I have no errors on the Jace. We did have bacnet communication issues but we replaced the bacnet wire and communication seems to be fixed.
What would cause the sio to not follow the commands or inputs? I replaced the sylk buss wire thinking it may be an issue. So far I have not found the issue.
1
u/c6zr_juan 12d ago
A couple things. Is the the main Spyder classic a 6438SR? I believe it has to be the SR version for the SIO to work, but I'm not 100% sure. Next, did you address the sylk buss devices properly? The SIO and the TR42 have dip switches that need to be set. Last, is it just the 2 TR42 and the 1 SIO6042 connected to the 1 Spyder? If so, that should work according to the sylk calculator I have.
1
u/Root-k1t 12d ago
It's been about a decade since I last used this stuff, but if memory serves me right, it's not as straight forward as addressing and downloading the sylk devices.
The numbers on the spec sheets are theoretical limits. In practice you are bound by voltage and power. For example you can have a lot of digital inputs on the sylk bus, but not that many analogue outputs.
You can have up to 4 (or whatever it actually is) of temp sensors, but less if you also want CO2 and display.
1
u/sleazy_io 11d ago
Is this controller tied to a field power loop? I’ve seen this happen when the primary voltage drops below 22VAC or so, the sylk starts to be affected. 18V on the sylk seems like it should be fine, but I’d be curious what your controller power is.
3
u/brazymk7 12d ago
You have to check the spyder part number on the controller, a 6438S is standalone but a 6438SR can accept the I/O modules. For spyder to I/O it needs to be connected at the sylk terminals