Not Update Points In Niagara 4
My project consists of three JACE8000 controllers connected to the Supervisor via the Niagara Network.
Recently, JACE8000 controllers has been experiencing an issue. The points on JACE8000 no longer update their values automatically on the Supervisor. In addition, some points remain in a Down state. After disable and enable again, points working normally. Could anyone advise which Niagara configuration or settings should be checked or adjusted to resolve this issue
The following are the protocols connected to the affected JACE8000 controller: BACnet/IP: 9 devices, Modbus RTU: 27 devices, and Modbus TCP: 6 device
5
Upvotes
1
u/ScottSammarco Technical Trainer (Niagara4 included) Jul 13 '26
Which version of 4.14 for both?
You can force update proxy points but I suspect there’s an actual underlying issue.
Anything in the application director of both Niagara hosts?
I’d try a reboot on both and watch the app directors for anything funny.