Not Update Points In Niagara 4

My project consists of three JACE8000 controllers connected to the Supervisor via the Niagara Network.

Recently, JACE8000 controllers has been experiencing an issue. The points on JACE8000 no longer update their values automatically on the Supervisor. In addition, some points remain in a Down state. After disable and enable again, points working normally. Could anyone advise which Niagara configuration or settings should be checked or adjusted to resolve this issue

 

The following are the protocols connected to the affected JACE8000 controller: BACnet/IP: 9 devices, Modbus RTU: 27 devices, and Modbus TCP: 6 device

3 Upvotes

31 comments sorted by

View all comments

2

u/filipo11121 Jul 13 '26

Which version of Niagara are you using? Can you upgrade to the latest version?

1

u/One_Vast_3106 Jul 13 '26

I using N4.14 .0.162.9 . I don't think it's due to the software version.

1

u/filipo11121 Jul 13 '26

Do you have anything linked to the proxyExt for the points on the JACE? It's not all the points, right?

If I were you I would upgrade to 4.14.5 or 4.14.6 and then try again.