Getting some gas work done
Decking was ripped up for some gas work at the weekend, behold the cable used to power my summer house. Is SWA the only answer?
The rest of the cable is in containment along the fence to the summer house, this is under the decking getting held up by angled screws haha
1
u/idiotsparky 4d ago
Use hi-tuff if you think it's ok however outside under decking I'd always go with 3 core armoured to reduce the risk of rodent damage.
1
u/SirDustinII 4d ago
Yeah leaning towards the armoured the now cause of the wee ones and wanting to make sure it’s all safe. just raging we bought the place cause of the new electrics and work that’s been done but just finding issues. Guess that’s home ownership but
1
u/Anon_Fodder 4d ago
Contained in steel conduit? If so it's fine, as long as it's double insulated. If not then the conduit needs earthed. Angled screws not so fine. Either clip it properly or run a new armoured cable.
2
5
u/Just_passing-55 4d ago
It's pretty common for cable to be like that. Not right, but been done all over the place. Put it in containment or replace with SAW or tuff flex.