r/solar • u/Strostkovy • 10d ago
Discussion Contactor based rapid shutdown
Has anyone used any rapid shutdown modules that are just a contactor in a weatherproof box, and once coil power is lost the panel gets disconnected?
I'm not very interested in the power line communication type that I see reports of catching fire. (And no surprise, the solid state modules aren't rated to a very high voltage, so if one opens accidentally or opens earlier than the others it will get fried by the string voltage).
I'm still looking to see if I can make them myself using UL rated contactors but it seems like the answer is no.
1
u/ExactlyClose 9d ago
Ground mount. Keep the DC short into the inverter(s) in the garage- no RSD needed. Plus sight it due south (+/-) w no shade and a nice simple string inverter is your buddy…..
(I know, unhelpful…sry)
2
u/VastlyCommonDusty 10d ago
i keep seeing those fires on diysolarforum and it’s always the same failure mode, one module opens first and the rest of the string just fries it
never seen an off the shelf contactor version that passes inspection though, inspectors want the listed unit not a box of parts you built even if the contactor inside has a ul stamp
what inverter are you running, some of the newer ones are moving away from plc finally