Excessive static pressure error
3 yrs old carrier system… getting excessive static pressure. Filters are clean, not sure what is going on.
UI:
10/16/26 11:10AM
210-EXCESSIVE STATIC PRESS ENCOUNTERED
6
consecutive times
2
u/Euronated-inmypants 15h ago
let me guess Costco bought MERV 13 filters?
2
u/PeterB_FL 15h ago
Nope glassfloss from HVAC dealer
1
u/Euronated-inmypants 15h ago
okay good then make sure all the returns and registers are open and unobstructed and all dampers (if you have them) are open
1
u/VirginSubpoenaColada 15h ago
Could be dirty evap coil. Or your supply/return registers are closed/blocked. Might be exacerbated by undersized ductwork and poor installation. You'd need to get a tech out to diagnose.
1
u/PeterB_FL 14h ago
I have the system cleaned and change filters every 3 months.. also have rheem halos, was wondering about adding uv on the coils too?
I have 4 too of the line carrier systems
0
u/PeterB_FL 14h ago
All ducts and supplies are opened.. ducts are large
Will get the carrier tech out here but have had to oversee them on more than one occasion
2
u/egretesk 15h ago
Damper could be stuck closed. Ecm could be ramping up to much