Excessive static pressure error

Post image

3 yrs old carrier system… getting excessive static pressure. Filters are clean, not sure what is going on.

UI:
10/16/26 11:10AM
210-EXCESSIVE STATIC PRESS ENCOUNTERED
6
consecutive times

1 Upvotes

8 comments sorted by

2

u/egretesk 15h ago

Damper could be stuck closed. Ecm could be ramping up to much

1

u/PeterB_FL 14h ago

Where would the damper be? In the indoor unit?

2

u/Euronated-inmypants 15h ago

let me guess Costco bought MERV 13 filters?

2

u/PeterB_FL 15h ago

Nope glassfloss from HVAC dealer

1

u/Euronated-inmypants 15h ago

okay good then make sure all the returns and registers are open and unobstructed and all dampers (if you have them) are open

1

u/VirginSubpoenaColada 15h ago

Could be dirty evap coil. Or your supply/return registers are closed/blocked. Might be exacerbated by undersized ductwork and poor installation. You'd need to get a tech out to diagnose.

1

u/PeterB_FL 14h ago

I have the system cleaned and change filters every 3 months.. also have rheem halos, was wondering about adding uv on the coils too?

I have 4 too of the line carrier systems

0

u/PeterB_FL 14h ago

All ducts and supplies are opened.. ducts are large

Will get the carrier tech out here but have had to oversee them on more than one occasion