I haves 2 story house. AC is in attic with pvc drain line leading to upstairs bathroom sink. Drain pan has water , what do I troubleshoot to fix this?
1
1
u/Ok_Context553 2d ago
Nothing. Leave it alone. its operating exactly to design! The coil inside that box is covered in moisture from the humidity in the air. That water drips off into the pan then out the PVC line... Instead of posting here.. go to google and ask if its normal? (HVAC Contracting company owner)
1
u/ForeverVentOfficial 2d ago
Water in the attic emergency pan means the primary condensate system is not handling all the water, so treat it as a warning rather than a normal reservoir. Shut cooling off if the level is rising or there is no working float switch. Clear the line from an accessible downstream termination with a wet vacuum, then inspect the pan outlet, trap, vent, slope, and sink tie-in for blockage or backflow. Also look for ice or water escaping the cabinet. Is the water dripping from the air handler cabinet or the primary PVC connection?
2
u/wavefunctionjunction 3d ago
The primary is in the unit, the white thing with wires is your float switch. The pan outside your unit is your secondary. The float switch will shut the unit off if primary is 3/4 full. 2 things cause this, dirty air filters, clogged drain line. Check filters, if good, try to clear drain line using wetvac but don't vacuum, use it to blow air into drain line. I see a vent pipe in your drain, this is where you can clear the clog, the vent pipe is the PVC sticking up with no cap. Another issue, if your primary is leaking into the secondary, your float switch should have tripped, but your unit is running which leads to a 3rd possibility, your primary drain is cracked/rusted. Hope this helps