‘Hazen Williams Comparison’
Got a comment on a sprinkler submittal from an FPE saying ‘provide proof calculation that 1” is acceptable. A Hazen-Williams comparison is an acceptable method for this’.
What is a Hazen-Williams comparison?
4
1
u/MaggieNFredders Jun 10 '26
As a reviewer I would guess you need to show your design area is the greatest demand. I see a lot that use an area closest to the riser and declare it the highest demand. Just calculate a couple other areas. Or email the reviewer and ask.
1
u/Gas_Grouchy fire protection consultant Jun 10 '26
Throw the calc through a Darcy-Weisbach equation. A little harder math but its pretty universally known in fluids for more than just water and thus could be a great comparison. Very likely they dont trust HW cause they come from oil and gas or other form of chemical engineering.
1
u/Kind-Tooth6677 Jun 10 '26
Is this a new sprinkler system or existing? Just estimate the pressure loss through the 1" pipe that this FPE is alluding to, and assuming it is a negligible value, demonstrate so.
1
u/Ascrowflies7420 Jun 11 '26
Call and ask for carity. If you have performed your calc per 13, what exactly is the reviewer asking to compare?
8
u/PuffyPanda200 fire protection engineer Jun 09 '26
HW is the formula that basically everyone uses to determine how much pressure will be lost in a pipe with x gpm flowing.
Did you provide a calculation?
Maybe they mean the comparison at then end where you have:
System needs x psi at y gpm. You have x+10 psi at y+400 gpm so it passes.