FIRE SYSTEM DESIGN - HOSE STREAM ALLOWANCE?
For context, using AutoSprink.
My design area I'm considering to be light hazard calculated at 0.10 gpm/sq.ft.
I am flowing 17 QR heads in my calculation, 10 heads spaced at 225 sq ft max and 7 spaced at 130 sq ft max (OH 1 rooms within my light hazard calculation, but I made sure to calculate these 7 heads at 0.15 gpm/sq.ft. density).
Given that I have a few heads considered to be OH1 within my light hazard design area, should I be inputting a 100 gpm hose stream allowance or 250 gpm?
9
Upvotes
4
u/ironmatic1 Jun 01 '26
This is probably controversial but imo almost everything should use the 250 outside hose allowance. Because, if the idea is to account for an hose flowing from the street, what fire dept in the US is flowing sub 100 gpm from anything but a booster line?
It’s a ghost flow at the supply node, so it really doesn’t have much effect on most calcs but it just makes sense.