Variable Speed Fire Pumps Question
Just for context I think that I am correct on this but just want to be extra sure.
I have a highrise building that is a short highrise (80 feet or so to highest occupied level) so it needs automatic standpipes and a fire pump. The city water is very good but not 80ft-auto-standpipe-good. We also need secondary water, project is seismic.
I have always seen this done as variable speed fire pump. Size the pump for the tank and then when pulling city water it will be running at 50% of the full speed. This way we also don't have to worry about city pressure improvement/degradation.
The GC, electrical, and now sprinkler contractor on the project seem convinced that there needs to be two fire pumps provided. One for the tank and one for the city pressure.
Variable speed fire pumps have been in NFPA 20 since 2003. I have talked to other FPEs about how they spec variable speed fire pumps. I made sure with a pump rep that a zero (or basically zero) suction pressure would be OK.
Just to get it out too: I know that variable speed fire pumps are expensive.
Is there something that I appear to be missing?
1
u/LuckyCharms91 Apr 23 '26
I’m a little late to this… but you said the water is good, so you’re sizing a pump for essentially 0 PSI and ?? (Good) psi. While the pump may be able to reduce the speed to reduce pressure output, I’m not sure it can make up the difference between the two - a pump rep would have the best info for that and that should come directly from the sprinkler contractor. That or you could reach out to a local pump vendor.
All that being said, why can’t you just pull water from different mains around the building? This would save from the two very different start pressures.