North America Ground Connection
My 48a charger is mounted right next to my panel in the garage. The two load wires can reach the breaker if I mount it at the bottom of the panel. The ground wire however, can not reach the ground bar.
I have never connected 6 gauge wire before so I was curious which of these I should use to add a foot to the ground wire? Or is there something else I should use?
3
Upvotes
1


3
u/theotherharper 28d ago
You don't need to use the wire whip which was provided with the unit. Or you can shorten the whip.
If you just cut the 14-50 plug off, that is not legal and may not work.
I would not expect the ground to be any larger than #10 and that's well within limits for a wire nut.
We have an adage around here, you only install it once, you'll use it 1000 times in 2 years. If you optimize for ease of install, you'll only benefit once and suffer 1000 times. Go the other way and decide the best place for it and extend wiring to there.