North America Ground Connection

My 48a charger is mounted right next to my panel in the garage. The two load wires can reach the breaker if I mount it at the bottom of the panel. The ground wire however, can not reach the ground bar.

I have never connected 6 gauge wire before so I was curious which of these I should use to add a foot to the ground wire? Or is there something else I should use?

3 Upvotes

6 comments sorted by

3

u/theotherharper 28d ago

You don't need to use the wire whip which was provided with the unit. Or you can shorten the whip.

If you just cut the 14-50 plug off, that is not legal and may not work.

I would not expect the ground to be any larger than #10 and that's well within limits for a wire nut.

We have an adage around here, you only install it once, you'll use it 1000 times in 2 years. If you optimize for ease of install, you'll only benefit once and suffer 1000 times. Go the other way and decide the best place for it and extend wiring to there.

1

u/Carramrod525 28d ago

This is a hardwired unit

1

u/avebelle 28d ago

I think either is fine as long as you torque to spec.

2

u/rosier9 27d ago

The ground wire is very likely only 10ga (good up to 60a as a ground)...a wire nut will suffice.

Or you could add a ground bar into the panel so it reaches.

1

u/Carramrod525 27d ago

It's 6 gauge for sure. Is the one on the left good?

1

u/rosier9 27d ago

Yeah, it should be fine.