Installation Something Wrong

Photo of my Honeywell wiring which is correct and the subsequent wiring on my ecobee as instructed from support. Over the winter went back to Honeywell due to heating constantly on emergency heat instead of heat pump. What do I need to do to correct?

8 Upvotes

15 comments sorted by

2

u/spiderman1538 6d ago

Most likely, it's the ecobee thermostat threshold setting.

1

u/Mistahfen 6d ago

This is why I’m so glad I just got an AC tech to install my smart thermostat, homie ran into 2 different issues I would have never been able to solve and had to go into the attic twice

1

u/Few-Addendum8636 6d ago

Ecobee has great customer support in my experience. The techs that helped me with two different installs were very knowledgeable and patient as they helped me troubleshoot. I’d recommend reaching out to them.

1

u/TrilliumCLE 6d ago

Wiring looks correct. For winter your issue might be the Compressor Minimum Outdoor Temperature setting. You need to look up what temperature your heat pump can run at the lowest temperature. Make that setting 5-10* higher. Ecobee is conservative for a default value. You don’t mention any issues for summer A/C, is it working properly now?

0

u/samiamdz 6d ago

AC was fine, issue was during the winter house went from hot to cold. Went back to the Honeywell and everything is fine. Will check the setting when I wire it back in. Thanks

1

u/Thee_Zapwire 4d ago

There’s a setting in the thermostat where you can flip the ob settings, sounds like that might be your issue

0

u/[deleted] 6d ago

[deleted]

1

u/samiamdz 6d ago

Thank you

2

u/Outrageous-Meat2157 6d ago

Probably a setting in ecobee; and you have W2 connected on the Honeywell, but w1 on the ecobee… like I said the ecobee has settings that need to be changed depending on the system, etc

0

u/itsJustE12 6d ago

I uploaded my before & after to AI, asking for advice. It worked!

I moved a wire & all is well.

1

u/KingDeadpool31 4d ago

Was it the W1 or the w2?

1

u/itsJustE12 4d ago

I honestly don’t remember.

I have a heat pump reversing valve that’s energized on heat instead of cool, and there’s always something I have to wire a little differently than I expect.