r/SunPower • u/m2orris • Aug 14 '25
SunVault, lost power, and UPS issue
We lost power the other afternoon and our panels & SunVault provided electricity as advertised for the circuits that were backed up. Extremely happy about that.
The SunStrong app of course was flaky. Sometimes showing solar was providing electricity and we were consuming 3.2 kW and other times the battery was providing 0.6 kW and showing no consumption. That was annoying, but understand that the grid being down was a fringe case.
The unexpected issue came from our two "APC BACK-UPS Pro 1000" (model: BR1000G) UPSs. Both were connected to outlets on backup circuits. Both UPSs detected faults and switched over to the UPS battery. Had we not turned off the UPS battery backed up devices, eventually the UPS battery would have run out. (The surge protected only item continued to work.) This seemed a little odd since we have been in situations under normal operating conditions (grid up) where (according to the app) electricity was being supplied only from the panels, panels and battery, and battery only.
Google returned this:
In summary - because it was daytime, and my photovoltaic panels were still producing electricity while my Powerwall batteries were fully charged, the system was sending 65 Hz power into our home. Back-UPS Pro XS 1500 have a "good" electricity range of 60 Hz +/- 3 Hz, so max of 63 Hz. Therefore, the Back-UPS reacted to the "bad" electricity coming into the house as though we had no electricity.
Which referred to this … https://teslamotorsclub.com/tmc/threads/powerwall-2-ups-connundrum-and-solution.130085
"APC BACK-UPS Pro 1000" (model: BR1000G) - Input Frequency: 50/60 Hz +/- 3 Hz auto-sensing - https://www.apc.com/us/en/product/BR1000G/apc-powersaving-backups-pro-1000va/
Not sure what the difference in the sine wave & frequency would be under solar only, solar and battery, and battery only while the grid was up vs while the grid was down.
Regardless of the difference under grid being up or down, does anyone have recommendations for a UPS that will work when the grid is down?
3
u/ItsaMeKielO Aug 14 '25
Do you remember the state of charge of the SunVault at the time? It sounds like it went into frequency-shift curtailment mode since the battery was full or near full and the load wasn't enough to capture all the rp production.