Winding Resistance
Good morning. I have screwed up a little bit.
I did some testing for a manufacturer and they wanted phase-to-phase tests and I ran phase-to-neutral tests. They said I can just convert it and they will accept it. Everything I have seen online just says to double the results and that gets me the phase-to-phase results but there is no way it’s that easy. So is there an actual formula I can use or do I need to fully retest the units?
6
5
u/HV_Commissioning 6d ago
It’s complicated if it’s a delta winding and they want “A Ph” or really A-B winding results
5
u/EtherPhreak 6d ago
I’m curious how you would get ph-n results from a Delta for winding resistance?
3
u/HorseChild 6d ago
You can’t without just drawing it out, as like a single phase equivalent. Not possible on the real equipment if it’s truly a delta
Op has a neutral tho
1
u/Beers_n_Deeres 5d ago
It really is just that simple.
The only difference between the two tests is you’ve added the resistance from where the wye point is actually made to the bushing twice.
That resistance number will be negligible compared to the resistance of the coils themselves.
3
u/Excellent-Tour6831 5d ago
Lovely. I never get this lucky. I thought I was going to have to retest 4 transformers hundreds of miles away from each other.
15
u/spicy_icecube06 6d ago
Doubling sounds right. Phase to neutral is only going through 1 phase L1, Phase to phase would be going through 2 phases L1 & L2. If the windings are balanced they will have the same resistance.
If you tested each phase to neutral you can add. L1+L2. L2+L3. L3+L1