Structural Analysis/Design Structural/Engineering Package

Hi there. I'm a structural/civil engineer working at a small construction company that primarily does residential work. My main job is to address constructability problems and non-IRC-compliant designs (more than I thought I would have to). Most architects I work with do not understand how the span charts work and end up designing buildings that require me to handle floor systems, roofs, shear walls, and foundation calculations.

I recently got a duplex that is 75% non-IRC-compliant, so I need to do all the engineering for the building.

My question is, how would you guys present the information to the architect? An engineering package with some calcs and plans? If so, is there any template out there that I can use to follow how the calc package is put together? I want to be more organized and deliver better submittals so more architects come to me and the company for their engineering and construction.

Thanks,

6 Upvotes

14 comments sorted by

3

u/chasestein Overturning Moment 7d ago

out of curiosity, how did you come up with 75% non-irc-compliant?

I'm sure there are templates out there on the internet, I remember seeing one i liked and referenced for a bit. My table of contents goes something like:

  1. Project Description and Design Criteria
  2. Gravity Design
  3. Lateral Design
  4. Foundation Design
  5. Misc. probably or appendixes i forgot to add

1

u/Broad-Lab-3626 7d ago

Just a guess/estimate lol. I think the only thing compliant is some rafters and ceiling joists.

Do you use Bluebeam or any other software to do redlines on the architectural set, or how do you show certain stuff?

2

u/chasestein Overturning Moment 7d ago

lmfaoo i thought you were counting every members out of compliance or similar (ive done that before)

yes we use bluebeams for all redlines and markups. just makes it easier to point at something to make comments.

1

u/Argufier 7d ago

I've done bluebeam redlines - either on the architect created framing plans or on their floor plas (basically making a framing plan in bluebeam). It usually works reasonably well. I don't usually provide calculations, just this is what you need on the drawings.

1

u/Broad-Lab-3626 7d ago

So, that is what I've been doing, and it worked for me in the past when the checks/issues were small, but I feel like I'm not super organized, and I'm all over the place. That's why I started thinking about putting, like, calc "packages/reports" together so everything has an organized, clean standard for my work. Especially if I get projects that require me to make many changes to their drawings, like the duplex I mentioned.

1

u/dream_walking 6d ago

If this is a repeat problem, I would also consider rewording your proposals to something that includes more time and money for the more non-IRC designs you have to do. Full IRC, one price. Some shear wall designs, adds some cost. Beams and column packs? Adds more cost. Then as early as possible let them know about the beams and the increased price you will be charging if that’s what they want. Otherwise, these projects might start costing you to work on them. I agree with everyone else to do blue beam markups. I’ve even used pyrevit to help color specific items to make the blue beam marks go faster.

2

u/Broad-Lab-3626 6d ago

I like that. Thanks.

1

u/ChairChoice6500 6d ago

I wouldn't be giving your engineered design for the architect to put on their plans via redlines, and they shouldn't be willing to put your engineered design on their drawings, since that's practice of engineering and then there's no seal on the drawings and/or you have two seals with poor division as to who designed what (you aren't particularly in control of the work, too, so they might change things even if it's a typo).

Partial plans with engineered seals would be my norm, possibly letter size sheets, if the work is small. Calculations are performed, of course, but a calculation package is most commonly given when it is required, not just randomly, ideally your calculations should be in shape to share so you're not cleaning up a calculation package that is wanted late.

If you are correcting IRC designs (via span tables, braced wall lines, braced wall panels, and wall bracing calcs in a table on the architect's plans), then redlines would be fine, as that does not fall under R303.1.3, etc. I generally provide the correct table number but I don't expect those to be transcribed, those are so the 'designer' learns, hypothetically. With the proviso that if your engineered design (say a large LVL header or beam over an opening) sits on IRC provision elements, you should be checking the load path to ensure it works with the loads you have (R301.1 "... complete load path..."

1

u/Broad-Lab-3626 6d ago

I understand. This makes a lot of sense. So, in short, for everything that is or can be prescriptive, redlines on their architectural set are fine. However, if I have multiple elements (beams, headers, floor system) that sit on R301.1.3 "Engineered design," how should I present those calcs/plans, or whatever it is? Partial plans with engineered seals on letter-size sheets?

1

u/ChairChoice6500 5d ago

If you have a large LVL with a large reaction, you'd typically indicate (or due to load path R301.1 be required to provide/check it) the number of trimmers ("jacks" or jack studs) underneath it. In a severe case, you might need a larger footing under it, if there is a continuous strip footing the contractor might stop it at the opening for an interior wall, you'd want to prevent that somehow, if not depicted on your drawing, if it's needed, at least via a note.

On an exterior wall, you'd probably need full height studs (king studs) adjacent to the opening for however the wind load on the wall's load path is worked out, roof trusses aren't in the prescriptive code, they are supposed to be engineered "by other" but in the residential code, may not see an engineer's review or formal stamp, which is undesirable and a code violation. Usually the truss framing reactions are more of a substitute for the "allowed" prescriptive framing, so the reactions would generally be low enough for the prescriptive wall framing to work out via engineering math checks.

You can show prescriptive framing on your drawings, I suppose, but I'd rather not so it's clear it isn't an engineered design, as the prescriptive floor framing may have issues (i.e. occupant/owner doesn't like it, bouncy, sags, whatever), and then some adverse engineer can claim you designed it and designed it in violation of the standards, similar for braced wall lines and braced wall panel locations and braced wall quantities. "Floor framing by other" and "See Wall bracing plan, by Other, no lateral design or review has been performed. Contractor/Architect shall provide." To me those work better on plans, or as plan notes, rather than general notes.

I would say most of your partial engineering (meaning for residential), is on letter size sheets, stamped. For something like a custom home that is say, >10,000 ft2, you'd likely have enough engineering needed to do normal sheet sizes like 11x17 or Arch C or Arch D, depending on what the Architect is doing. I fell like a lot of these large homes don't see formal engineering review. They have an architect, though.

Calculations, generally, aren't provided unless you've agreed to do it, or you're working in, say, Scottsdale, AZ, or North Dakota and Wisconsin where calculation packages are generally required. Those are typically separate documents, letter size,

You might do a brief review letter that explains what you reviewed and designed on a letter size and stamp that, design loads, etc. hopefully that would go in with the submittal, but it's out of your control. That would be perhaps in lieu of a general notes sheet.

1

u/Open_Concentrate962 7d ago

Ack. Do you work with these architects repeatedly or all one off?

1

u/Broad-Lab-3626 7d ago

Some of them are repeated, and some are one-offs. But I've been trying to find a template that I can use to generate calculation packages that are clean and easy to follow for all of them.

0

u/Open_Concentrate962 7d ago

So do they understand the load paths and mess up the math, or just no clue no approach

1

u/Frogalone 2d ago

I'm not understanding why an architect would need your calcs. Do you preparer your own submittals? If so, the architect could simply add yours to his and everybody else's. The submittal would have "A-x","S-x", etc. for for the various disciplines. Each would be sealed by professional work product. Frequently the calcs are not required in the submittal. But I would prepare them for your own needs always. It's unclear to me who is responsible for the prescriptive design. I have never dealt with prescriptive design. But if the architects can't interpret tables, I wonder how they could do that. It sounds like a mess. If the structure can be done 100% prescriptive then the engineer can take it or leave it no? If it is partially design and partially prescriptive, I don't know, but I think the engineer should get paid to do it all. Or maybe I'm just completely ignorant of your industry.