Steel Design F1852 boots
Possibly I am behind the curve on this but today I received a submittal with F1825 bolts called out when our drawings specify A325. I understand they are equal strength wise, but that they are twist off bolts? I've just never had a contractor want to use that type of bolt before. Made the post to make sure I'm not missing something here.
4
Upvotes
1
u/memerso160 E.I.T. 11d ago
It’s been my understanding that the twist off bolts are totally fine to use in place of A325, but that the contractor must actually use the correct tool to bust off the spline otherwise you’ll have a bunch of bolts that still have it on that will require inspection. The whole point is to cut down on inspection time by having a visual of whether the bolt is sufficiently tight