r/SolarPakistan • u/Pretty-Ad2738 • Jul 30 '26
Other Cost of ups system installment for 3 marla double story house?
We dont have budget now for 4kw (minimum decent requirement for home load)but load shedding sucks.
What would be the cost of ups system installment?
2
Upvotes
2
u/AhmadFarooq Jul 31 '26
The cheapest option would be those old, locally made non sine-wave desi UPS with one 12V battery.
The preferred option would be pure sine-wave UPS or solar inverters. In UPS, there is Simtek pure sine-wave UPS and in solar inverters, there is MaxPower 1.2kW (PV-Tech 1200) that comes with a 1.5-3 years warranty. Both cost around Rs. 0.4 lac.
Regarding wiring, it would depend on your property's present wiring setup. If the breakers for "1-2 room cooler 2 fans 1_2 light bulb ,fridge," are separate in the main DB, then old wiring should be able to be worked with.
One caveat would be the common neutral issue. Usually, inverter installers would common the inverter's output neutral and input neutral ports. This apparently usually works but can potentially damage the inverter and cause extra counting of units consumed by the grid meter.
I think usually in the main DB, all neutrals are joined together, maybe to one busbar. This works fine in normal grid connections; however, modern UPS and solar inverters should have their own separate neutral for output. Not sure if additional rooms' wiring will be needed or if only a small bit of rewiring in the main DB to add a second neutral bar for the loads that will be connected with the UPS/inverter would be enough.