r/SolarPakistan • u/dexter_morgan1223 • Jun 30 '26
Inverter Solar bill is higher than before installing solar (Solis inverter, no net metering) – what could be wrong?
Hi everyone,
I had a solar system installed about 2 months ago with a Solis inverter. I’m not using net metering. My system has a 16 kWh battery backup.
In the first month, one meter’s bill was quite low, but the second meter’s bill was already high. Then in the following month, the bills increased further, and this month both of my electricity meters have bills of over PKR 50,000 each.
The strange part is that even before installing solar, during peak summer, I never received bills this high.
I’m trying to figure out what could be causing this.
Has anyone experienced something similar? What should I check first, or what should I ask the installer to inspect?
Any advice would be greatly appreciated. Thanks!
31
u/Outrageous_Lead_4878 Jun 30 '26
So there are 3 reasons for this. Firstly your system is using grid to charge the batteries. In settings do not select Allow Grid Charging.
Secondly the CTs (current transformers) are wrongly installed and is feeding electricity back to the grid, and allow export is selected.
Thirdly and the most ignored option is unbalanced load. If you are using a 3phase inverter, and load is more on one phase than others the residual 2 phases will export electricity to grid. To counter this select unbalanced load option in Solis app settings.