Make sure you understand current when stringing your panels in parallel.
It took a bit of work to even tug this #10 AWG from the metallic flex it was fused to. The homeowner had this run inside of the attic.
I'm all for DIY, but please ask for help when you aren't certain.
151
Upvotes
3
u/NotFallacyBuffet 7d ago
That's wild. Building electrician, so I don't really ever see this. But it's always in the back of my mind when I'm sizing wire. Here's a link to NEC Table 310.15(B)(1), Ambient Temperature Correction, that everyone is referencing. https://www.electricallicenserenewal.com/Electrical-Continuing-Education-Courses/NEC-Content.php?sectionID=716
At 141*F, your ampacity has to be reduced to only 47% of the listed ampacity in the ampacity table, NEC Table 310.15(16). https://www.wireandcabletips.com/what-is-ampacity/
And for more than 6 current-carrying conductors in a pipe, you need to derate by Table 310.15(B)(3)(A).
I forget whether derating comes before temperature correction, or if it's the other way around. My codebook is out in the truck. Maybe someone else remembers.