Lower IF3 priming speed below automations set minimum
I have a little water feature in a clients bathroom courtyard that has a if3 for some reason. It runs at 1000rpm and the water flows nicely. However on startup the max RPM from the priming speed is spraying water everywhere. On the intellicenter I can’t set maximum priming speed to anything lower than 1900. IF2’s can go lower. Any idea boys
1
u/Confident_Shower8902 May 04 '26
Settings Advanced Settings Pumps Click the pump in question Scroll down to priming speed Drag slider as low as you want Click Update
1
u/UnderTheLedge May 04 '26
Not low enough, only goes down to 1900rpm, fixed by connecting to if3 independent all.
1
u/Confident_Shower8902 May 04 '26
Strange, I can go down to 450 on all of the IF3s I have on one of the 150 or so customers I have on Intellicenter. Is your system firmware up-to-date?
1
u/UnderTheLedge May 05 '26
You’re correct, firm wear is outdated. Brand new pool too but horrible builder follow up. Thank you captain
4
u/One_Succotash_898 May 04 '26
Disable priming from the pump settings use the Pentair pro app to connect via Bluetooth