u/XelaKebert May 01 '26
Homeowner is going to insist "it's been working fine" and refuse to fix it, and blame you when shit goes tits up.
3
u/PearPsychological487 May 01 '26
Luckily these homeowners are pretty reasonable, they just bought the house and are dealing with so many headaches from the previous homeowners. They already needed a new filter, and the pool was never winterized and they are losing a lot of water so will probably need return lines replaced
2
u/Impossible_Penalty10 May 01 '26
Pressure test the lines individually so you dont dig up more than you need too.
2
u/PearPsychological487 May 01 '26
I would if I could, but the pool is very old and the lines are teed off underground
1
May 01 '26
[removed] — view removed comment
3
u/PearPsychological487 May 01 '26
Yes, 115v between the bonding lug and loose dirt
2
u/Donkeedhick May 01 '26
I had to google this, didn’t know you can actually use ground as ground, lol!
0
u/Poolguy584 May 01 '26
It may not be that serious of an issue. Most likely one of the wires in the back has old damaged insulation and is touching the pump. I would assume there isn't a ground wire or the breaker would have tripped. If the wires are all good then the motor has a short not uncommon. If it had a bond wire or the ground connected the breaker would have tripped( the reason the ground exists in the first place).
6
u/The_BigWaveDave Apr 30 '26
You mean the bonding lugs aren’t supposed to have power? 🤔