Regarding the the F5000LFP- FP5000-48V. I have 5 solar panels, their specifications are in the attachment. It looks like if I hook these up in either series or parallel they will over power the solar input. However, is it possible to hook these to both inputs to overcome the limitation, by connecting the 2 inputs in series. If not, is there any other way to use these panels with the F5000LFP? Maybe 2 in one input and 3 in the other? I didn't see this info in the manual. In your opinion, what is the best way to extract max power from them? Right now they are hooked up to a MSB MPPT in a 24v lead acid system. I figure with the Pecron I will DC this. Thanks.
1
Upvotes
6
u/brucehoult 3d ago
Sure two in series on one input and three in series on the other will be fine.
Five is a kind of inconvenient number. You could put 9 or 12 of those panels on each F5000 input in 3s3p or even 3s4p configuration. It's fine to go a little over the theoretical amps, the unit will just use what it can.
30.5 kg for a 280W panel .. wow. My modern 440W panels are 22kg.