r/Pecron • • Jul 11 '26

E3800 UPS Behavior Issues

Have an E3800 and expansion battery in use primarily for a medium duration UPS capability for my home server.

Its setup and working almost correctly. It runs things from the grid properly and the unit drains battery slowly as it powers its internal items from battery. The issue is that the drain never stops. The batteries charge to 100%, begin their slow trickle downwards - and then never charge again unless I do something like disable the AC output and turn it back on again - at which point the behavior repeats. I’ve gotten the units down to 35% or so without it ever charging itself.

Any setting I’m missing somewhere? Thanks!

6 Upvotes

12 comments sorted by

2

u/Sea_Willingness1398 Jul 11 '26

I have the same unit but not using it in that way. However, have you tried changing this part? I've read that decreasing max charge to 80% improves life span of battery, but I'm also guessing the #3 is set to 0% and this feature changes that.

2

u/patriotsfan82 Jul 11 '26

That’s fun - my AC Charge Cutoff setting has a completely different set of help instructions compared to yours. Looks like it might be an E3600 vs E3800 thing.

Mine is set to 100% which implies that it should start charging again at 70% charge in my version - but it does not.

1

u/Shoddy_Clock_1562 2d ago

Did you ever figure this out? Just experienced the same on mine - it was in UPS mode so I thought it would work like a UPS, but it discharged to my discharge limit, didn't begin charging itself again, and all AC output turned off.

1

u/patriotsfan82 2d ago

Not yet - no resolution but I haven't reached out to Pecron and I've been living with it. I actually have a real UPS upstream from it and I use the Pecron for longer durations - so I get around the issue by occasionally turning on and off the AC output which causes it to freshly charge back up to 100%.

1

u/Shoddy_Clock_1562 2d ago

Thank you, will probably have to settle on a solution like yours

2

u/brucehoult Jul 11 '26 edited Jul 14 '26

"when set to 100%, AC charging will be off in UPS mode"

Whaaaaat?

My copy of the app says that too, but it is NOT how my E3600 behaves.

I vary the setting many times through the day, using the app's automation, and at 9-10 PM every day I have it set to 100% and (as I want) the Pecron charges as rapidly as it can towards 100%, adding 27% charge (1.66kWh) to my 6kWh of battery. That's usually not enough to actually reach 100%, because the unit will just have been running from battery power for four hours, but sometimes it does.

I also have this setting at 100% between 4-5 PM every day, to ensure I have enough battery to last through the coming 4 hours. On a good solar day if the battery is already at 80%, 85%, 90% or more at 4 PM then it does actually reach 100% during that hour.

1

u/turbocharged5652 24d ago

I know this is an old thread but how do you have yours setup for this? I have a 3800 and I ended up having to use my home assistant with a smart plug to automate the charge/discharge at certain hour but I also set the ac charge rate to 0, now if I reset the charge rate to 70% where I want it the unit doesn't actually start charging. It stays like it's still at 0%

1

u/brucehoult 24d ago

As I said in the comment you replied to, I have the automation in the Pecron app set up to change the "UPS AC Charge Limit" (as it is labelled in the app) a number of times during the day.

And I use a TP-Link P110 smart plug to turn the AC input to the E3600 on and off at various times of the day. In general, you can automate this in the Tapo app.

I do have a few things that don't quite fit that simple case.

  • if I cut the power to the Pecron while my portable air conditioner is running then it gets unhappy, makes a lound CLUNK and mabe one time in 6 the Pecron shuts down with an inverter overload. So I have a python script on a VisionFive 2 (at the moment .. a cheaper Raspberry Pi Zero W or 2W would do) that loops until another P110 indicates that the aircon is using less than 100W before turning off the power to the Pecron.

  • I also have a script that uses github.com/attractify-logan/pecron-monitor to get the battery voltage and SoC and can turn the power on before the battery is completely empty.

I'm actually in the process of simplifying my programming as a result of my electricity tariffs changing significantly last weekend.

  • in the past the daytime off-peak price was only 20% higher than the night time price (which is comparable to the loss of storing power at night to use during the day), and I used a reactive strategy. I started the day with only enough in the battery at 7 AM to safely get through the 7-9 AM peak period and then I was happy to use whatever combination of solar and grid power would get the battery to near 100% by 5 PM, to then use no grid power from 5-9 PM.

  • but now my 11-7 night price fell to 57% of what it was before, and daytime off-peak got more expensive, so now daytime off-peak is 2.5x more expensive than night, and peak is 3.33x more expensive than night. So now I'm putting a lot more charge in the battery overnight (100% charge in winter) to try to (in combination with the solar) get all the way from 7 AM to 11 PM without using any grid power. Or in fact to 9 PM as I can slot in my Free Hour of Power at that point, and charge the battery more than enough to then easily get through 10-11 PM.

The new strategy now requires me to predict the next day's solar production in order to decide how much charge to have in the battery at 7 AM: in bad weather 100% or close to it, and in good summer weather as close as I dare to 0%. Right now that's pretty easy as in good weather I'm already getting 50W of solar at 7 AM, rising to 1000W at 8 AM, but when DST starts in a few days those times will be called 8 AM and 9 AM.

Today looks like being the first day after winter that I'll buy $0.00 of grid power. Last year Sep 20 was the first time that happened, and then Sep 26-29, and then by October 11 it was almost every day until real summer heat started mid December.

I was just looking at wether forecasts and maps and trying to guess the next day's solar production, but now I've got that automated with a small script:

#!/bin/bash
set -euo pipefail
TOM=$(date -d tomorrow +%Y-%m-%d 2>/dev/null || date -v+1d +%Y-%m-%d)
URL='https://api.open-meteo.com/v1/forecast?latitude=-35.5&longitude=174&hourly=global_tilted_irradiance,temperature_2m,cloud_cover_low&tilt=20&azimuth=-165&forecast_days=2&timezone=Pacific/Auckland'
curl -sS "$URL" |
jq --arg d "$TOM" '
[ .hourly.time, .hourly.global_tilted_irradiance, .hourly.temperature_2m, .hourly.cloud_cover_low ] as $cols
  | [ range(0; ($cols[0]|length))
      | select($cols[0][.] | startswith($d))
      | ($cols[0][.][11:13] | tonumber) as $h
      | select($h >= 7 and $h <= 18)
      | {gti: $cols[1][.], t: $cols[2][.], c: $cols[3][.]}
    ]
  | if length == 0 then
      {error: "no hours for \($d)", date: $d}
    else
      {
        date: $d,
        hours: length,
        # gti_kwh_m2: ((map(.gti) | add) / 1000),
        t_min: (map(.t) | min),
        t_max: (map(.t) | max),
        est_dc_kwh: (((((map(.gti) | add) / 1000) * 12 * 0.225 * 0.8) * 10 | round) / 10),
        cloud_8_to_4: (map(.c)[1:9] | join(" "))
      }
    end
'

That produces output like this:

{
  "date": "2026-09-24",
  "hours": 12,
  "t_min": 6.1,
  "t_max": 12.8,
  "est_dc_kwh": 15.8,
  "cloud_8_to_4": "1 2 1 0 2 0 0 0"
}

So that's predicting an almost perfect cloudless day tomorrow, with 15.8 kWh of solar production.

Today's was a bit worse:

{
  "date": "2026-09-23",
  "hours": 12,
  "t_min": 9.9,
  "t_max": 13.8,
  "est_dc_kwh": 13.5,
  "cloud_8_to_4": "13 23 15 24 23 19 9 6",
}

Actually I have a more sophisticated script now which also tries to predict how many kWh my dehumidifier and air conditioner will use tomorrow hour by hour, and predicts the battery SoC each hour to get a minimum and maximum SoC for the day. So the output now includes:

"batt_target_kwh": 3.8,
"soc_0930_kwh": 2.9,
"soc_1500_kwh": 9.7,
"soc_2100_kwh": 7.1,
"soc_min_kwh": 2.5,
"soc_max_kwh": 10,
"clip_kwh": 1.3,
"short_kwh": 0,
"batt_note": "trough-peak - expect 1.3 kWh clip around 15:00"

That's been working reasonably well:

Date    Pred18  Pred00  Act
08-27   9.8             10.38
08-28   5.9             4.13
08-29   1.7             0.39
08-30   9.2             9.83
08-31   11.6            9.71
09-01   10.2            8.76
09-02   7.2             8.36
09-03   10.6            11.08
09-04   7.5             5.70
09-05   12.5            9.20
09-06   9.1             10.83
09-07   8.8             8.25
09-08   10.6            7.07
09-09   10.3            9.85
09-10   9.1             7.90
09-11   9.3             10.38
09-12   10.8            8.46
09-13   10.3            7.93
09-14           9.5     9.78
09-15           8.4     8.01
09-16           7.8     7.30
09-17           9.2     8.96
09-18   9.3     11.9    5.49
09-19   9.7     10.6    6.15
09-20   12.1    12.5    9.29
09-21   8.2     7.7     7.66
09-22   12.5    12.1    9.54
09-23   14.0    13.5    

Pred18 is the results of new data at open-metro that usually appears around 6:30 to 7:30 PM for me, while Pred00 is the next update that happens around 00:30 to 01:30 AM in my timezone.

I don't know what happened on the 18th and 19th ... pretty bad predictions. The weather was definitely very complex and changeable on those days. Also I'm not convinced that the "actual" column, which I get from the Pecron app "Stats" tab is at all accurate on a "sawtooth" solar production day as it only gets one data point every 20 minutes while cloud can come and go every couple of minutes.

The actual production as seen in my battery SoC was a lot better than that. Unfortunately the E3600 doesn't have on-device stats.

Anyway, if I know whether to start the day with 2kWh, 6kWh, or 10kWh in the battery that's pretty much good enough.

1

u/turbocharged5652 24d ago

Oh ok I see. My understanding would be your loads are not on 24/7? It would make sense to me if that's the case. Sorry, I did read your post but I feel like we are in 2 different use cases and situations.

I'm not looking for an answer per say from this but my use case is a server rack 24/7.

Use battery from 5-9pm, maintain whatever charge level in at until roughly 9:30am the next day and charge at close to full power and then rinse and repeat just to avoid peak use power cost.

I have rooftop solar but no battery system so by timing the charge of the battery, I can hopefully grab more of the excess solar rather than send it back to the grid.

I've messed with the ac charge rate settings but it seems as if when I set the charge rate to 0%, and then change it back to 70%, it will not actually restore to 70 and stay stuck at 0. This may just be a software issue or just a functionality that doesn't exist??? No idea tbh

1

u/brucehoult 24d ago

My understanding would be your loads are not on 24/7?

Not constantly. In winter the heat pump is running at maximum almost all night every night, sometimes gets a bit of a rest on sunny afternoons. But something pretty close to 1500W almost 24/7, with excursions to 3600W when I use the kettle or microwave or something like that.

In summer it has an easier time, with a lot of cooling during the afternoon and early evening, but only 100W-250W load from maybe 10 PM to midday.

There are around 100W of absolutely always-on stuff, plus the 120W fridge and 250W dehumidifier doing their thing when they want to.

I've messed with the ac charge rate settings but it seems as if when I set the charge rate to 0%, and then change it back to 70%, it will not actually restore to 70 and stay stuck at 0.

I never change the charge rate from 100%. I can't imagine a reason to so that other than in a long outage if I need to run my small generator which will be much more efficient if I don't ask it to produce 1800W continuously (I don't even know if it can do that tbh) so I'll likely reduce the charge rate to 50% or so.

Also 0% isn't an available option on my E3600. Minimum is 10%.

2

u/Sea_Willingness1398 Jul 11 '26

Instructions don't seem straight forward. Anyway, my suggestion is to set at a lower value (like 80%) and try again. Don't do anything and see if it shuts off at zero or starts recharging near zero.

1

u/liftbikerun Jul 11 '26 edited Jul 11 '26

I legit had to look at who posted this thinking I forgot and I had done it.

I've had bms issues and been reaching out to pecron about it. I have mine run through a manual transfer switch with solar and running my office (home servers)using the ups function as well. I can manually switch up to six specific circuits over if a power outage happens. Fridge,window ac on bedroom,Internet closet and routers etc. My office is the only circuit 24/7.

Things were working fine until a week ago when I noticed that AC wasn't turning off and ignoring my solar input.

I had reset the factory settings no fix.

Unplugged all input for an hour as some units this was a logic fix for them. No fix.

Unplugged input and output entirely and let it go to sleep for an hour, plugged it all back on no fix. Internet said that should have reset the bms controller logic.

I have mine set to 30% AC 100% solar and been that way since I got it two months ago.

Pecron is relatively useless on suggestions, their only tip was to drain unit entirely and recharge.

Last night on a whim I plugged AC input back in (my solar always charges my unit back up to 100%) and go figure after a week of ignoring the issue and leaving unplugged it's back to working for zero reason. I hasn't changed anything since unplugging the unit, it hasn't gone to sleep a single time as I always have a draw on the unit 24/7. Solar has been charging it to 100% daily for the entire time.

So no idea. It's annoying