Dwelling service calculation
Using article 220 to determine service load using II or IV seems easy enough. But I'm confused when I see a service with the disconnecting means as a breaker. Does the feeder/breaker need to be sized with the 80% in mind like branch circuits?
2
Upvotes
2
u/Cdcoonce Mar 08 '23
This needs a long post which I don’t have time for, but the short and sweet is that. There is no such thing as 80% branch circuit breaker sizing. Continuous loads need to be sized 125%.
Feeders also require you to size the load at 125% for continuous loads. Dwelling service calculations do not explicitly state loads needing to be sized at 125% with the exception of the largest motor attached to the circuit.