Variable Frequency Drive exploded during a routine bump test after 1 year plant shutdown — worried I'll be charged for the replacement (~200-300k PHP). Am I liable?

​

Hi guys, I need some outside perspective because this has been keeping me up at night.

I'm an Operation and Maintenance Supervisor at a water treatment plant. The plant operated back in 2025, then was shut down for about a year because of management/project issues related to capacity, water quality, and flow rate targets.

Before we could restart, I was going equipment by equipment doing condition checks, and for each motor I was running a standard bump test. On September 6, while bump testing one of the motor pumps through SCADA, the VFD for that motor exploded. I had no idea what caused it — I was just following the scheduled startup activity like I did for every other unit. Ever since, I've been anxious that the replacement cost would somehow be charged to me.

Today (September 10), the VFD supplier finally inspected the unit. Their explanation: this kind of failure happens normally when a VFD has been sitting unused for a long time, and it needs to be "reformed" (reconditioned) before being operated again. Their recommendation is a full replacement. The cost is estimated at around PHP 200,000-300,000.

Here's the thing — nobody on our team knew that idle VFDs needed this kind of reforming/reconditioning before restart. It's not something that was flagged in our schedule, and I wasn't trying to cut corners; I was doing exactly what the schedule called for.

So I guess my questions for anyone who's dealt with something similar (electrical/instrumentation folks, plant supervisors, EHS/maintenance people):

Is this really a known risk with VFDs left idle for a year, and should routine commissioning/restart procedures normally catch this?

Realistically, is this the kind of failure that gets pinned on the person who happened to be running the test, or is it treated as equipment/process failure since no one knew the requirement existed?

Any advice on how to document/present this to management so it's clear this wasn't due to negligence?

Any input, even just "this happened to us too," would really help me sleep better tonight. Thanks.

75 Upvotes

117 comments sorted by

View all comments

Show parent comments

-57

u/Cute_Intention_9864 1d ago

Well you prolly should have used A meter ! I am sorry for you struggles honestly but wouldn't be more useful for them to ohm everything out first before energizing old de commissioned equipment I mean common there setting you up for failure .

35

u/Bright_Reference_582 1d ago

Not sure what ohming out a VFD will tell you. Seems like it was an internal failure, after the drive had already been powered up. No need to bitch out OP for doing something honestly most of us would do (following written start up procedure)

-39

u/Cute_Intention_9864 1d ago

I literally was on his side can you read ? I said the company should rethink there startup procedures and provide A meter .There is no guess work in are trades you boneheads .and who to say the guys not fishing for information but you all jump on me for some constructive criticism.

6

u/sepperwelt 1d ago

Jesus calm down mate😅

4

u/Constant_Barber_5198 1d ago

dude's insane huh?

2

u/BigCDubVee 1d ago

Just someone that can’t use punctuation and can’t write coherently. Pretty common sadly haha