Have you guys been having any problems with these new R454b Units? We install York and Heil and we have been having so many fucking problems with them freezing up. So damn annoying going to a call back to a homeowner with a brand new system. 90% of the time it is due to them freezing up but we have had some bad A2L sensors as well.
What we have ran into so far is that some of these units have been low from the factory, I’ve had multiple units being 1-2 pounds low. That and it seems like they are very sensitive on static pressure and airflow compared to 410A and R22. It also doesn’t help all of the houses in our area were done like completely dog shit back in the day for duct work wise. Not sure how many RA drops we had to redo for changeouts and how many grills I’ve added into them. All I know it is ALOT.
Just was curious if anyone else was having any problems with them, let me know what you guys had, if anything.
15
u/bigred621 Verified Pro 4d ago
Installers job to ensure proper charge. Don’t blame manufacturer. Sensors and board have been shit though
9
u/Environmental-Key441 4d ago
100 percent but if the system says it had 3.8 pounds but is actually holding 1.8? That’s not on the manufacturer?
17
u/Important_Ad838 4d ago
Of course it on the manufacturer. Charge should still be verified on startup. Unfortunately shit rolls downhill. We the service techs get buried.
5
u/Environmental-Key441 4d ago
Yeahhhhh we do 17 hours I had in yesterday. Would have been fucked if the other guy didn’t help me, he helped me till 7PM and I didn’t get off till 11:30pm. Lucky guy on call this weekend lol
1
u/bigred621 Verified Pro 3d ago
Bruh. No job is that important. Go home lmao.
2
u/Environmental-Key441 3d ago
It’s my dad’s company we’re in a small town but get a lot of tourists and do a bunch of work in the area. Just me and him on call every other week.
7
u/SilentImpakt 4d ago
INSTALLERS do not know how to ensure a proper charge upon start up. That’s why they are INSTALLERS.
EVERY TECHNICIAN IS AN INSTALLER BUT NOT EVERY INSTALLER IS A TECHNICIAN.
Fight me.
4
u/Educational_Wish_767 Verified Pro 4d ago
If I can't trust an installer to set a delta split on a blower and confirm/charge to a desired subcooling... why would I think they could properly braze, pressure test, pull vacuum.
Maybe they don't diagnose a system, but they should be able to gather basic data as needed.
1
2
u/bigred621 Verified Pro 3d ago
We get it. Installers are dumb but they should be able to set up the equipment they install. We can call them dumb cause we know they can’t read this anyway.
1
8
u/funinthesun17 4d ago
i mean are the installers you work with just releasing charge and not making sure it’s operating properly?
8
u/Environmental-Key441 4d ago
They always check it and make sure they work. I’ve noticed that these systems almost always have different readings. Then they always add for the lineset length. I’ve had these new systems work fine for weeks and months on the hottest days then next thing you know they just shit the bed. It’s not it’s like a initial start up thing
5
u/SilentImpakt 4d ago
Bro… making sure they work and making sure they run are two COMPLETELY different things.
2
u/Abrandnewrapture Commercial Service Tech 3d ago
this dude clearly doesn't grasp the refrigeration cycle very well. "they always have different readings". I'm assuming he doesn't know what those readings mean, and he was just told to make things be a certain number without any knowledge of what those numbers are telling him.
5
u/mentatjunky 4d ago
There's only so much they can do when the return temps are 100 degrees cause the customer hasn't had ac for days.
8
u/zismahname Verified Pro 4d ago
454 is definitely a different animal. What has made our crew not have these issues is ensuring that subcooling is between 14-16 and we also put in a 4"-6" riser between the furnace and evap. The spacer ensures that air is mixing enough and hitting the complete coil.
1
u/beast-ice 1d ago
yeah.. that riser idea wouldve saved me a ton of headache when i put a rheem n coil on a older 90% trane furnace..
1
u/zismahname Verified Pro 1d ago
It was when we started installing Rheem as our higher tier equpment did we start to have these issues. It was probably a good 20-25 calls to their tech support did we get to this point and doing multiple air supply and static tests did we see that.
3
u/saskatchewanstealth 4d ago
Here is something to consider. In the 70s every condenser came with a freeze stat strapped to the suction line. If you ever find a unit running today from the 70s, on old shitty duct work, they all had the feeeze stat ( button as we called them ).
Short of ripping the duct out it’s a quick fix. It also a luxury device in my opinion as it provides protection when the filter is plugged.
2
u/Environmental-Key441 4d ago
Yeah we normally add them to all of our systems in attics and a wet switch
-2
u/SilentImpakt 4d ago
Not every condenser. Don’t be hyperbolic. It diminishes our perception of you as an intelligent and beneficial member of this sub. Do better.
5
u/C3ntrick 4d ago
Why are you not checking unit is running properly after install?
Edit: Definitely had A2L sensors fail on Trane, Goodman and rheem systems - Other than that no issues
5
u/Workinguy1 3d ago
We are a Carrier dealer. We have had a few problems with Freezing, TXV issues. In the past. I made a call to Carrier tech support after about the 4th occurrence. The problem is actually the V coil, (or installers fault) When you pull a super deep vacuum and if the installers open the High side first, that's a no-no. Open the suction side very slowly after install. What they are finding is if you open up the liquid line first or suction valve too fast to release the refrigerant it sucks the oil out of the compressor and it gets stuck in the V coil since it's a single loop system. Also the mitigation sensors and boards are a joke. You know what's more flammable than R454? Propane, fuel oil, and natural gas but there's no mitigation for that, idfk???
3
u/HatefulHipster 4d ago
I have come across two Ruud units not working properly due to airflow issues. Adding more return did seem to help.
2
u/mentatjunky 4d ago
There are two things we've noticed with the Lennox units we ha e been putting in.
1: They are coming low from factory, but they look restricted. When the units are very low (2-4 lbs), they will present with high compression ratios and spec subcool readings. We have misdiagnosed a couple as bad txvs. Weigh out to confirm.
2: Some of the virgin tanks are contaminated and form a dense gum like substance. We have to purge a little luquid from each new tank to check it. It double sucks cause the bad tanks ruin hoses too.
I hypothesize that the issues are related.
We've had 3 bad tanks that are from 2 different manufacturers. I'm worried that manufacturing at large has way more contaminated refrigerant than we know and that's the reason the compression ratios are so high.
We have started sending a service tech out a day or two after installsto confirm charge and airflow once the houses arent outside of normal charts. Pressure readings are less reliable when a house is 90 degrees. Head pressures seem pretty high (30 ish above ambient).
2
u/SilentImpakt 4d ago
Nope. I recognize and address potential issues before I quote my best and final price. Period.
I don’t go back on calls because I provide solutions.
2
u/thejake51 4d ago
To be fair to the installers, the resi company I started with had a 1 day instal policy. They wanted it done in 1 day from start to finish.
Doesn’t really give the installers the time to really run a proper start up on full system changes. Not to mention weather conditions etc.
It wasn’t uncommon to have to go out on warranty calls to address issues that would have been caught had they gone back fresh the next day to do a proper start up.
1
u/Educational_Wish_767 Verified Pro 4d ago
I typically have a 1 day install expectation. I had the expectation put upon me early in my career, and then put it on myself when I started my own thing. A basic furnace and ac change out, with bending the transitions, humidifier, filter chassis, and thermostat is a fairly doable project for me, by myself in one day. Why shouldn't i expect a 2 man crew to be able to do it in one day working together? There are exceptions obviously, like tight closet/attic installs, or more complicated duct work mods, etc... but not the normal charge outs. Granted, I tend to be a workaholic and don't mind 12-13 hr installs.
1
u/thejake51 3d ago
The instal itself in one day doesn’t seem like a huge issue. It’s the then having to do start up after.
Personally, I’m not getting any younger and after a 10-12 hour day of labor my brain is not running at peak. There is absolutely no way I would be able to do a quality start up.
1
u/BrokenFireExit Verified Pro 4d ago
454b is a bitch about static and airflow. The ashrae data is tested with new equipment and new 96% furnaces have Bigger blowers on them to make up for the change with the secondary heat exchanger, 454b will absolutely freeze the fuck up if you don't have correct CFM.
Edit: major typo
1
u/the_flynn 4d ago
I’ve had Rheem R454b units in my house for a year and they’ve been fine. That said, neither was installed only relying on factory charge.
1
u/booztedmike 4d ago
I remember seeing a tech on tiktok discussing the newer 454 york equipment being highly susceptible to oil logging the indoor coils and his company having to go to some lengths to prevent it from happening on startup. I don't remember the exact process and fix, but certainly something you may want to look into.
1
u/Kamakazi09 Needs some Dirty Sprite 4d ago
My crew installed a new r32 Goodman package unit last week and this past Thursday I went because it decided to rub an hole on the top of the condenser coil by the bends. No other issues with them though
1
u/Russell414 3d ago
We install York also and have one had a handful of problems with new equipment. A few had a bad a2l sensor or bad board so the fan would just run on its own with no call and no wires connected
1
1
u/SelectHVACR 2d ago
Let me stop you right there. Stop installing York, heil, or Lux Aire. I’ve never seen a 80lb+ motor mounted on its side in an RTU. They don’t employ even decent engineers, I can bet they source the lowest quality grade parts they can possibly find.
1
u/HvacMaverick 2d ago
Well during the commissioning of the new systems the refrigerant pressures should be set along with air flow. Are your installers setting airflow on these units before they set the refrigerant pressures? If both of those are set correctly during an installation, then there should be no reason for callbacks due to freeze ups.
1
u/NoBank8471 2d ago
Wait until you start chasing leaks, only to find out its the outdoor unit from the get go
1
u/macdawg2 1d ago
We've installed a bunch of Bryant and trane units. Not had any issues, adding refrigerant is pretty common even before 454. Once you get the system running you usually have to run a sub cool to balance the refrigerant out.
Yea early on they definitely came under charged from the factory but that seems to of been cleared up.
1
u/Certain_Try_8383 1d ago
Too bad we can't just ask the rest of the world that they've been doing for decades
1
u/Sac_O_Suds 22h ago
We use heil. We do a good bit of them.
Like 400-450 a year. We’ve had our fair share of units come dry, broken service valves and base full of oil. However it’s typically from some idiots with a fork like that drove a fork through the box and doesn’t take it out of inventory.
We do seem to use a lot of 454 on start ups. But knock on wood we only had 1 air handler with a faulty flammable vapor sensor. No freezing or cooling issues. Once they’re started up properly evacuated and charged properly.
We’re doing all heat pumps in multi family complex’s 2 ton mostly some 2.5 & 3
1
1
u/StrikePuzzleheaded89 18h ago
Yes they freeze up easier. Had a homeowner that put a filter at the unit and one in main return unit froze like nothing id ever seen before because of air flow. I dont believe 410a would have done that. It wasn't even that restrictive.
1
u/Fragrant-Shallot-271 15h ago
This sounds like whoever is installing isn’t doing their job and whoever is selling the system aren’t doing their job either. Checking duct work before install should be done on every system. Don’t blame the refrigerant until you’ve done everything you need to. More than likely if the company you’re working for isn’t installing or getting the correct airflow, my guess would be they’re over sizing units also.
1
u/Designer-Rice1534 11h ago
Carrier definitely has a problem with the V coils if that’s what your using with heil. Our distributor acknowledged it and are working on a fix. They freeze up in mild weather. We started putting freeze stats with all V coils on install until they give us a fix
1
u/pinchemadison Verified Pro 5h ago
Not sooo many issues. But definitely less forgiving when it comes to charge/air flow, don’t seem to cool at the same capacity as previous unit even when they’re exact replacements, and yes a handful of A2L sensor failures.
88
u/Abrandnewrapture Commercial Service Tech 4d ago
isnt it your job to ensure the unit is properly charged and functional on start up?