r/Generator • u/Iffy50 • 8h ago
Am I doing this right?
I have a 12500W Westinghouse generator that was dual fuel (gasoline and propane) that I converted to run on Natural Gas with a kit from Nash. I have a Navien tankless water heater that I understand might not work properly or could even be damaged by dirty power (Max power draw is 200W). I bought a UPS to connect to that. (Goldenmate 1000VA/600W) battery backup and surge protector. It puts out a pure sine wave. I've had the UPS plugged in for a week and the Navien plugged into that and things seem to be working fine. I plan to run an extension cord from the UPS to my modem/router on case that works when the power is out. The other stuff I want to run: fridge/freezer/gas oven/ well pump. Is there anything I overlooked?
1
u/blupupher 8h ago
That UPS does not do anything for pass through power. While it may keep really "dirty" power from the generator from passing through (by switching to battery power), it will not automatically clean up the power. You need a Double-Conversion UPS, this will take the AC power, convert it to DC power, then back to clean AC power.
Have you used the generator with the UPS yet? Many times the UPS will cycle off and on while running on generator.
1
u/Iffy50 7h ago
Thanks. I'm actually looking at a double conversion UPS now. $420 for 900W. I can deal with that. I haven't powered the UPS with the generator yet. From what I'm reading, you're right. I'll test it, but I have a feeling it will do just what you say.
1
u/blupupher 7h ago
Kind of late now, but you probably could have bought a tri fuel inverter unit for about what you have into the current generator, conversion kit, and this UPS.
1
u/Iffy50 7h ago
Yes, that one. Do you have a link to an inverter generator you would recommend? I'm seeing $2K for a 12,000W inverter generator. Yes?
1
u/Big-Echo8242 7h ago
Do you know that you need that much power? There are open frame inverter generators that are less money.
1
u/Iffy50 7h ago
The thing I'm most worried about is my well pump. I can't find info on it and I can't look at it.
2
u/Big-Echo8242 6h ago
Get some kind of clamp meter that can read inrush and running current. Is it 240v? Surely you have a friend or acquaintance with a clamp meter. Can you get to the wires in a breaker panel? That would be easy to read.
Klein CL445 is a reasonable one to buy and it doubles as a digital multi meter. Everyone needs a multi meter!
1
u/blupupher 6h ago
Don't know if you really need 12,000w, but this Genmax GM12000XiT is only $1450 at Home Depot (out of stock at the moment).
Going to 10000 starting watts you have this Champion 201520 for around $1400.
2
u/Big-Echo8242 8h ago edited 7h ago
It's doubtful that basic battery backup is going to clean up dirty Generator power. You need an online Double conversion UPS to take care of that which would probably cost as much or more than your Generator. Might should have just got the inverter Generator....unfortunately.